Search the forum,

riello

Riello is a municipality located in the province of León, Castile and León, Spain. According to the 2004 census (INE), the municipality has a population of 864 inhabitants.
other
riello ups is a multinational company its headquarter located in Viale Europa, 7 ZAI, 37045 Legnago (VR), and In India it is in Plot no. 213A, Sector-4, IMT Manesar, 122050 Gurgaon (HR).

View More On Wikipedia.org
  1. Gazzt

    Riello rdb oil pumps.

    Hi just to give you a heads up, i was commissioning 2 x oil boilers both with riello rdb pumps, when using vacuum gauge on vacuum port on the pump i had a oil leak after putting the allen key screw back in. Here is the problem, the rubber seal which is green is slightly too big and while...
  2. G

    Riello oil pump - water in system - advice

    Hello All, I'm having a nightmare with my Riello Oil Burner - pump. My own fault initially - I tipped the tank a bit as new oil wasn't coming for a few days - this caused the pump to fail - water and gunk into the system. Tiger Loop full of gunk too. Replaced pump after 900 litre oil delivery...
  3. M

    Grant combi external riello pump problem

    Morning guys I installed a new Grant 26e external combi just after Christmas. The oil supply was on a temporary supply from an ivt tank which was new and clean. Cross land filter as per installation as always! after around 2-3 weeks the burner locked out and on inspection it was humming with no...
  4. B

    Riello RDB Pump Needle (Solenoid) Valve

    Hi Can anyone tell me how much travel there should be on the "plunger" of the Valve, the one I currently have fitted seems to have virtually none, also should the plunger and stem be able to be separated for cleaning? Mine can't..... just trying to establish if it is jammed and needs replacing...
  5. D

    Riello RDB2 90-120 not firing after power cut

    Hi, our power tripped and the boiler wouldn't fire after this happened, I bought a new photocell as this failed some years ago, however I have noticed recently that on start up it has made a noise like a slipping fan belt, not exactly a squeal but it's there, I changed the photocell and it still...
  6. L

    Riello control box problems.

    Been having problems with the grant combi boiler 21e locking down and the button on the control box needing to be pressed to fire up the boiler. An engineer was called out and he said it was likely to be the photocell, which he cleaned which allowed it to work about an hour, then it locked out...
  7. M

    Riello pumps

    Hi all Anybody had or know of new or old pumps having problems with new oil from suppliers i.e. Seizing up etc? cheers
  8. Robert Tyrrell

    Replacement for Riello pump on Camray 5

    Got called to a breakdown this morning and the pump is stuck so needs replacing. Does anyone on here know of a Danfoss replacement for the Riello pump that OEM on this? I don't mind fitting another Riello but I only carry spares for Danfoss as that's what I usually have to deal with.
  9. N

    Riello RDB Red Lockout

    Hi Guys I have had this several times where the oil boiler's red lockout light comes on, this time it was due to low water pressure in the system. I have topped this back up to spec but the red lockout light is still on. If i press the illuminated red reset button nothing happens. It doesnt...
  10. R

    Riello motor stopping or jamming

    What causes a burner motor to jam on start up. Give the fan a push and away she goes.
  11. C

    Riello Photocells

    Anyone else getting a lot of failures on new(ish) 3008646 PECs ? I've just had to change yet another on my own boiler and had quite a few in the last couple of months...
  12. J

    Riello RDB and bentone oil burners

    I have a Riello RDB burber and a Bentone burner for sale, both removed from working boilers, looking for £80 each, open to offers Both totally complete with their pumps all the little bits. Located in crawley
  13. W

    Riello RDB burner motor running but not firing - tip

    Had this come up again last week, and just wanted to pass on this tip: If you come to a Riello RDB burner which has the motor running but does not attempt to fire, or takes a long time to fire, it can either be the photocell or the motor. Most often it is the photocell. To test, pull the...
  14. G

    Riello 171T motor help

    I bought a replacement 171T motor, the new one ahs a five wire connection, the old one a four wire. are they compatible ? what is he correct connections for the new version ? any ideas ?
  15. A

    Riello oil pump question

    will a Riello mectron ( short stem and plate on top ) oil pump work satisfactorily on an RDB burner many thanks dave
  16. C

    oil pump on riello

    fitted a new one, old one was seized , replaced bearings in motor and cleaned the fan whilst I was there to make sure all was spot on , but its still humming and not turning, it does work when I switch it on - off and reset it , but only half the time, what would it be? capacitor?
  17. G

    Riello Control unit

    Hi, I have a Boulter Classic boiler,the burner control unit is a Riello RBL G5 443T58. My problem is anintermittent start up. The burner starts as normal and runs, cuttingoff when the operating temp has been reached (as normal).This carrieson for a few cycles. The system then locks out...
  18. J

    Firebird C35 Riello RDB 2.2 problem

    Hi people. i installed the firebird c35 today and as I was going through the post purge on the burner it lit for a good five minutes before I turned down the temperature control at the boiler then the burner cut out and the central heating pumps kept working. No power seems to be getting to the...
  19. P

    best alternative to a Riello Gulliver diesel

    Hi, Hope business is good for everyone. Need your opinion: What is the best alternative to a Riello Gulliver RG1 diesel? Any tips appreciated :)
  20. T

    riello burner

    hi all im having trouble with a riello burner, when starting up it will just ignite for a few secounds then go out and ignite again for a few secounds etc, have checked ,solenoid,photocell,capacitor and control box all of which are working any sugestions please
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock