Hi just to give you a heads up, i was commissioning 2 x oil boilers both with riello rdb pumps, when using vacuum gauge on vacuum port on the pump i had a oil leak after putting the allen key screw back in.
Here is the problem, the rubber seal which is green is slightly too big and while...
Hello All,
I'm having a nightmare with my Riello Oil Burner - pump. My own fault initially - I tipped the tank a bit as new oil wasn't coming for a few days - this caused the pump to fail - water and gunk into the system. Tiger Loop full of gunk too.
Replaced pump after 900 litre oil delivery...
Morning guys
I installed a new Grant 26e external combi just after Christmas. The oil supply was on a temporary supply from an ivt tank which was new and clean. Cross land filter as per installation as always!
after around 2-3 weeks the burner locked out and on inspection it was humming with no...
Hi
Can anyone tell me how much travel there should be on the "plunger" of the Valve, the one I currently have fitted seems to have virtually none, also should the plunger and stem be able to be separated for cleaning?
Mine can't..... just trying to establish if it is jammed and needs replacing...
Hi, our power tripped and the boiler wouldn't fire after this happened, I bought a new photocell as this failed some years ago, however I have noticed recently that on start up it has made a noise like a slipping fan belt, not exactly a squeal but it's there, I changed the photocell and it still...
Been having problems with the grant combi boiler 21e locking down and the button on the control box needing to be pressed to fire up the boiler.
An engineer was called out and he said it was likely to be the photocell, which he cleaned which allowed it to work about an hour, then it locked out...
Got called to a breakdown this morning and the pump is stuck so needs replacing.
Does anyone on here know of a Danfoss replacement for the Riello pump that OEM on this?
I don't mind fitting another Riello but I only carry spares for Danfoss as that's what I usually have to deal with.
Hi Guys
I have had this several times where the oil boiler's red lockout light comes on, this time it was due to low water pressure in the system. I have topped this back up to spec but the red lockout light is still on.
If i press the illuminated red reset button nothing happens. It doesnt...
Anyone else getting a lot of failures on new(ish) 3008646 PECs ?
I've just had to change yet another on my own boiler and had quite a few in the last couple of months...
I have a Riello RDB burber and a Bentone burner for sale, both removed from working boilers, looking for
£80 each, open to offers
Both totally complete with their pumps all the little bits.
Located in crawley
Had this come up again last week, and just wanted to pass on this tip:
If you come to a Riello RDB burner which has the motor running but does not attempt to fire, or takes a long time to fire, it can either be the photocell or the motor. Most often it is the photocell. To test, pull the...
I bought a replacement 171T motor, the new one ahs a five wire connection, the old one a four wire.
are they compatible ? what is he correct connections for the new version ? any ideas ?
fitted a new one, old one was seized , replaced bearings in motor and cleaned the fan whilst I was there to make sure all was spot on , but its still humming and not turning, it does work when I switch it on - off and reset it , but only half the time, what would it be? capacitor?
Hi, I have a Boulter Classic boiler,the burner control unit is a Riello RBL G5 443T58. My problem is anintermittent start up. The burner starts as normal and runs, cuttingoff when the operating temp has been reached (as normal).This carrieson for a few cycles. The system then locks out...
Hi people.
i installed the firebird c35 today and as I was going through the post purge on the burner it lit for a good five minutes before I turned down the temperature control at the boiler then the burner cut out and the central heating pumps kept working. No power seems to be getting to the...
hi all im having trouble with a riello burner, when starting up it will just ignite for a few secounds then go out and ignite again for a few secounds etc, have checked ,solenoid,photocell,capacitor and control box all of which are working any sugestions please