As Tammy says according to the layout of the job. Also you've been away for a while ago from your domain. So hopefully the piping up is well lagged and the need for a speedy water recovery could get faster.
If there is an obvious long pipe run. The lagged pipework should be twice the lag closer to the hot cylinder for heat conservation reasons.
 
[DLMURL]https://www.traceheatinguk.co.uk/commercial-hot-water-maintenance-trace-h[/DLMURL]

I was going to suggest using this until I saw the cylinder pipework un-lagged (Not Part L compliant) so chances are none of the supply pipes are insulated.

Insulation would help on its own but if you want to use this heat tape to maintain the hot water temp in the pipes they must be well insulated. The pipe routes need to be located to work out if it is possible / cost effective to install a secondary return or self regulating heat tape but either way insulation of pipes is going to be required.

Get a good plumber in, unfortunately it is your responsibility to ensure that the installation is notified to Building Control (hot water cylinder AD Part G & L1b & heating appliance Part L1b
sounds like bathrooms as well Part H, electrical Part P etc)

Was there planning involved ?
 
Last edited by a moderator:
Oh my gosh, the plumber has replied and all he said is nothing can be done about it now. I just have to live with it.

I cannot accept this. I have paid thousands for a new heating system and I am in a worse position than when I had my little combi boiler. I never had an issue with the time it took to get hot water only sufficient supply.

I instructed private building control from the start of the project. Before we moved back in the Surveyor came by and did a final inspection. Should he have picked this up?
 
After a new heating system is installed, is it normal practise for the plumber to carry out a test to see how long it takes for hot water to come through?
 
Who employed the plumber, you or the builder?
Who designed and specified boiler etc
 
The builder.
I believe the plumber designed the heating and hot water system as he is the most qualified person to do this - not 100% sure but it does not make sense for the builder to do it.

I said I wanted a boiler and a separate hot water cylinder due to the supply issue that I had with my combi. From my research I believe that combi-boilers are designed for flats rather than three/four storey houses. I said I wanted a Vaillant boiler as I hear they are one of the best.
 
He is aware and sticking by with what the plumber has said.

I have called Vaillant and they think it is to with the design of the pipework. They said that the fact that I am getting hot water means that the boiler is working.
 
It won't be a problem with the boiler, it will be either a very badly designed pipe layout or fault.
 
Either way, it's the builders responsibility to get it fixed if you're paying him and he's paying the plumber.

I've said it before, and I'll say it once more, get a decent plumber in to look at this!
 
I will do that. Could you recommend a decent plumber? Please PM me if you prefer not to post their details.
Thank you so much!
 
Give Mak a call on:

07899747777 his rates are £90 ph plus vat and I would expect him to find what's wrong in less time than it takes the kettle to boil.
 
Please do. He's a lovely fella and will give you an honest and frank opinion of what the problem is, who's to blame and how to get it fixed to your satisfaction.
 
I'd like to draw your attention to this thread which you started in July last year: http://www.ukplumbersforums.co.uk/c...79-hot-water-circulating-ring.html#post791776

It's very disingenuous of you moan about the performance of your hot water system when your plumber advised you to have one AND you asked for our advice on here. We have endeavored to help you on a variety of subjects and you've received a lot of valuable AND FREE advice. I doubt very much that you'll see much more of that on here; well not from me anyway!
 
I feel dirty, abused & used.

Post 2 in the July thread gave you all the info required, you choose to ignore this (free) advice.

Go live with the consequences I say.

The cheek of some people to come back & ask what they can do about it now.
And then to try to blame it on the Plumber / Builder to boot.

Better give your mate the heads up Howsie they will probably try to knock him.
 
Last edited:
Okay, before you all get cross my posting in July doesn't tell you the complete story but I can understand why you would feel angry.

Back in July I received an e-mail from the builder which asked if I wanted a hot water circulating ring. He said in the e-mail "this is not necessary required as is only for comfort". If I chose not to have the ring then "hot water will start running in about 20-40 seconds" but if I chose to have the ring then "hot water would appear in a few seconds". This was in relation to the shower in the loft en-suite and the time it would take to get hot water. There was no discussion that the rest of taps in my house would be affected.

The price quoted was quite expensive to us which is why I posted on the forum in July to find out whether to do it or not.
Unfortunately, there were a number of unforeseen events that occurred which caused us to go over budget, for example my husband smashed the bedroom window by accident so we had to replace them. We discovered there was no insulation between the floor boards so had to add the cost of that in. When we took up the carpet in the bedroom we found that an old leak we had in the toilet had spread into the bedroom so had to replace the floor boards and so on.

As such we had to seriously look at areas where we could makes cuts and one of them was the circulating ring. We just thought, okay we will just wait 20-40seconds for the hot water it is not that long.
 
I hope that you and your builder come to a mutually satisfactory conclusion.
 
We based this decision on the information that he presented to us. Obviously if he said that I would have to wait 3+ minutes in the kitchen and all my taps would be affected I would consider this an necessity rather than a luxury item for comfort.

I spoke with Mak, really nice guy so thank Howsie for his details, he said that if it had been him he would have put it a secondary return into the design for a 3+storey house automatically and not even asked the client if they wanted it.

When I texted Mak I actually asked if he thought I was to blame as this is something that has been on my mind a lot. He replied back and said it was their fault because of the information that was presented to me.

I am very grateful for all your help and advice that has been given here. Of course I really, really regret not going ahead with the ring. My house is just finished, I have a baby and a young child, so the idea of the house been smashed up again makes me feel completely ill.
 
This posting started off with the question whether 3+minutes was normal to get hot water in the kitchen. I thought it could be to do with a setting on the boiler. I did not even connect it to the circulating ring because that, in my mind, was in relation to getting hot water in the loft so why would my kitchen be affected.
 
This posting started off with the question whether 3+minutes was normal to get hot water in the kitchen. I thought it could be to do with a setting on the boiler. I did not even connect it to the circulating ring because that, in my mind, was in relation to getting hot water in the loft so why would my kitchen be affected.

the longer the run the more cold water you have to draw off before fresh hot water from the cylinder is used, the pipe might not be lagged/ insulated

with a secondary return the cold water in the pipe is sent back to the cylinder and fresh hot water is put in its place

in simple terms
 
Thanks for explaining Shaun.

What I can't get my head round is why it takes such a long time to get hot water in the kitchen. I know the boiler has been moved from the kitchen to the Utility room but when the boiler was in the kitchen I didn't have to wait over 3 minutes to get hot water in the Utility room. The wait was more like 40seconds. My husband thinks the hot water must go to the loft first before coming back down to the kitchen in order to take that long rather than straight from the Utility room to the kitchen...

Hopefully it will all be resolved and this will be a story I will tell to my children when they are older about the dramas involved with renovation projects.
 
Thanks for explaining Shaun.

What I can't get my head round is why it takes such a long time to get hot water in the kitchen. I know the boiler has been moved from the kitchen to the Utility room but when the boiler was in the kitchen I didn't have to wait over 3 minutes to get hot water in the Utility room. The wait was more like 40seconds. My husband thinks the hot water must go to the loft first before coming back down to the kitchen in order to take that long rather than straight from the Utility room to the kitchen...

Hopefully it will all be resolved and this will be a story I will tell to my children when they are older about the dramas involved with renovation projects.

from the boiler to the kitchen distance wise? and very unlikely it will go upstairs first and then back down to the kitchen
 
It is around 8 meters away, is that big? The kitchen and living room is open plan so one room. The Utility room is next to the living room, so across the living room to get to the kitchen sink.
 
It is around 8 meters away, is that big? The kitchen and living room is open plan so one room. The Utility room is next to the living room, so across the living room to get to the kitchen sink.

depending on run you could have 10-12m maybe 15m if theres things in the way of pipework esp if its un- insulated yes

at a rough guess 0.2L per m of 15mm or 0.35L for 22mm

worst case 22mm estimated at 15m 5.25L
 
Sorry this doesn't mean anything to me. How does this translate timewise? Are you saying 3+mins is normal then because of the distance? If so, why didn't I have an issue with the time to hot water in the Utility room when the boiler was in the kitchen?
 
Sorry this doesn't mean anything to me. How does this translate timewise? Are you saying 3+mins is normal then because of the distance? If so, why didn't I have an issue with the time to hot water in the Utility room when the boiler was in the kitchen?

depends on factors length and run of pipework is it insulated etc, but building reg/water regs state you must have hot water within 30 seconds

"government guidance recommends that when opening a hot water tap, or other outlet, the water should reach 50°C within 30 seconds." to stop wastage of water
 
Do you know which section of building regs your quote came from so that I can refer to it. It does say it is only a recommendation though.

I had instructed private building control for my renovation project but the surveyor for some reason is not replying to my e-mails about this issue as I had asked him first whether 3+mins was normal before posting here.
 
Status
Not open for further replies.

Reply to Over 3 mins to get hot water in kitchen - is this normal? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
122
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
131
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
282
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...