Discuss Triton shower heater kettling query in the Bathrooms, Showers and Wetrooms area at PlumbersForums.net
Hi Guys Im on my third T100XR in quick sucession. The water heaters start kettling, making a banging noise. This happens after about 12 to 18 months of domestic use. Triton say they have never heard of the issue, probably as they would.
We are in a soft water area, mains pressure is good, and the AC mains is good too.
Any views on the subject.
Have you changed the hose and head of the shower from the stnd or added anything?
That’s strange and the water flow out is the same as before?
Can you measure the flow rate from the shower (e.g. by using a measuring jug and stop watch) and temperature rise relative to the incoming cold supply? Comparing these with the shower specifications might be worth doing. Also, check the pressure of the water supply.
Yes nothing has changed, the water pressure doesnt pulse either. The Mains electric is feed from a new 3 phase cable the size of my arm. Voltage is 230 nominal all the time.
Is this a domestic installation? I assume you have a 3 phase + neutral supply. I think it's possible that if the phases are not accurately balanced and/or there is an issue with the neutral you might be getting more than 230V delivered to the shower heater, which might be an explanation. Does your system have a monitoring box on the supply?
@Murdoch is the resident electrician so he may be able to give more/better advice if you post some more information about your electrical supply.
Ill do the temperature difference Chuck also check flow rate and physical water pressure. Note we have a TW10i on the same water main with no issues.
The 3 phase is not full 3 phase, only a single phase is live as they havent upgraded the tranformer yet. We are PME for the earth. Ive Fluke multi meter.
If I turn the shower temperature down the kettling decreases. Cold water flow, no kettling.
I’d get the incoming supply and circuit properly tested. The chances of 3 units being faulted is unlikely to say the least
does the circuit in question have RCD protection ?
The incoming supply was replaced in May 2021 with a new 3 phase domestic main - with 2 phases diabled as they awit a new transformer. The Board people tested the the voltage and the PME earth. The Consumer unit has a 30mA RCD which passes test unit an RCD tester. The MCB is 50 Amp. We never get tripping. The Mains voltage is 230V nominal.
The canary in the coal mine here is the Triton TW 10i that feeds a sink. Its on the same water main and consumer unit - no problems at all.
The current heating element was replaced by Tritons field service bloke. Initially he fitted an element that didnt heat the water enough. He paid us a second visit where he replaced the water heater, this time it was warm as new.
I have said to Triton on this and the last occasion, invesigate the water heater. They refuse, I small a rat. By water heater I mean the cylinder contraption in the guts of the thing.
Reply to Triton shower heater kettling query in the Bathrooms, Showers and Wetrooms area at PlumbersForums.net
Ah, the joys of older home ownership (1974). We thought our major plumbing issues were dealt with when we got rid of our orangeburg sewer line and...
2K
Hi, some professional advice would be greatly appreciated, We are having an Unvented Cylinder installed into our 2 bedroom ground floor flat. I...
9K
Hi, this is my first post, it might be a bit long because im trying to put all the info which could be relevant but i'll try to avoid waffling on...
3K
  • Locked
ok had a new unvented tank fitted and system changed from gravity to fully pumped. initially the plumber connected to the original gravity...
3K
Dotty
  • Locked
I MOVED INTO MY NEW HOME 3YRS AGO AND IN THE BATHROOM WAS A TRITON T80SI. THIS WAS EXISTING AND AFTER A FEW MONTHS OF MOVING IN THE SHOWER BURNT...
7K
PlumbBobBob