What does the internal bypass valve do in a Viessmann combi?

Discuss What does the internal bypass valve do in a Viessmann combi? in the Central Heating Forum area at PlumbersForums.net

Messages
40
Could someone please explain what is the function of the internal bypass valve in a Viessmann combi and how its settings MIN/MAX or malfunction somehow would affect operation of DHW and heating?
Thanks in advance.
 

Attachments

  • Screen Shot 2021-12-12 at 14.46.36.png
    Screen Shot 2021-12-12 at 14.46.36.png
    196.1 KB · Views: 30
When the boiler switches from hot water to heating the water moving has to go somewhere when the diverter switches over
 
It’s set to x pressure so when the diverter moves the system increases pressure and the bypass activates
 
Should be set so under normal operation it doesn’t open
 
The MIN pressure seems to be around 140 mbar. But what ist the opening pressure in the MAX position? I cannot find this information anywhere.
 
Vaillant have a internal bypass ( on the primary circuit) on all their system and combi boilers, it is factory set to 250mar but is adjustable from a minimum of 170mbar to a max of 350mbar, it provides the minimum flowrate required by the boiler at reduced flow demand and pump overrun after boiler shutdown, Viessmann setting may be similiar.
 