Hi

I'm hoping someone can help me out.

I have a POTTERTON PROMAX COMBI 28 HE PLUS A boiler which the manual states that the boiler utilises the primary side of the DHW plate heat exchanger as an automatic integral bypass.

I'm about to fit a Honeywell system which will place a TRV on all the radiators including the one in the living room which has the fixed position valves.

What I cant find information on is do I still need to fit an Automatic External Bypass Valve even though this Internal Bypass is mentioned. With the new Smart TRV's the condition will arise that all the TRV's close when no zone requires heating, turning off the boiler, but there is still the 3-minute pump Overrun to worry about.

Does anyone have experience with this?

Mike
 
If there is enough flow for the boiler to operate when producing hot water then there will be enough flow for the heating system by-pass through the primary side of the DHW heat exchanger
 
If there is enough flow for the boiler to operate when producing hot water then there will be enough flow for the heating system by-pass through the primary side of the DHW heat exchanger

Hi

Thanks for the answer, It's been interesting starting to understand the internals of the boiler.

I can see how this could act as a bypass during heating operating when TRV's start closing in and flow through the boiler reduces below the boiler required minimum flow.

I'm looking at fitting a Honeywell Evohome System, and for a fact at some point whether due to a TRV fault, a TRV requiring recalibration, or some other scenario, the Honeywell main controller is going to call for heat with no TRV's open. I was concerned that the internal bypass wouldn't be suitable to cover this scenario and that it might end up overheating or cycling too often or some other damage. There will be TRV's on all radiators.

There is also the 3 minute overrun after the boiler is called to shutdown. From what I can find on the Internet it's to allow the boiler to dissipate heat before stopping completely. Of course, half of what I read on the internet could be written by people with less of a clue than I have ;-)

Would this function still be carried out by the internal bypass?

Cheers

Mike
 

Reply to Do I need an External Bypass Valve in the USA area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
257
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
234
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic Pushfit seems to be getting better and better, cost and convenience was always better, but now the quality is to, have we reached a stage where plastic will...
Replies
2
Views
253
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
344
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock