Overheating Baxi 100 HE condensing boiler.

First of all switch that boiler off. It's DANGEROUS!! read on...

If you have met a Baxi 100 HE with a melted combustion chamber it’s caused by perished glue allowing the burner ceramic to lift and cause furnace-like volumes of gas/air mixture to enter the combustion chamber.


The ceramic face only becomes loose when it gets hot. When it does become loose it lifts and the fan responds by pumping a vastly greater volume of gas/air mixture into the combustion chamber. For the boiler I have just been investigating the working pressure dropped 3mb which indicates the increase in gas rate. I couldn’t measure the gas rate at the meter because it had overheated well before I could get there.

What seems to happen is the glue begins to fail and little by little the ceramic lifts - maybe over several weeks. So the boiler starts to run hot and I guess this contributes to the failure of the manifold O-ring and maybe even the flow switch. If you think about it, if there is overheating, it must be excess gas. It can't be anything else. The problem is that once the boiler shuts down the ceramic drops back onto its seat, the glue solidifies and amazingly it looks to all intents and purposes like a perfectly serviceable component.

The boiler overheats enough to melt and distort all the lower parts of combustion chamber aluminum and wreck the door seals - it cinders them. Then it overheats and shuts down usually via the fan stat. On stopping, the ceramic then drops back into the metal burner base. When it’s cool enough to handle the ceramic it's held rigidly in place again, sitting there all innocently.

About a year ago I was called to a 100HE and the sump of the
combustion chamber and 2 to 3 inches of the lower side walls had melted. It was a mess. I couldn’t think how sufficient gas had entered the combustion chamber to get so hot. Of course the ceramic element was sitting there looking secure in the pressed steel base.

A 100HE kept me baffled for a week. The flow switch had failed and the lower manifold was leaking just to add to the confusion. When to door came off the seals had gone but not cindered. I fitted new ones and left it running. This time it seriously overheated and melted the sump base. I thought I had not put the seals on properly causing the overheat. I talked to Baxi technical but they hadn't a clue. With a new base, flow switch and manifold O-ring in place the boiler overheated again (Arrrrgh!!). It quickly became red hot inside and it roared noisily. I didn't know what the roar was. There was some damage but not too much and so I ran it up again and watched very carefully. Initially the flame looked as it always had from cold - blue and fairly quiet (almost normal). And then bit-by-bit it started to roar and the internals of the combustion chamber turned cherry red. Then in an instant as it was really overheating I happened to see the ceramic lift. I couldn’t believe it at first but then it stuck half out and when it cooled down there it was, jammed solid but at an angle and finally revealing the problem.


I find it shocking that Baxi haven't recognised this fault. From what I see there are multitudes of these boiler breaking down like this and they could be salvaged just by replacing the burner every three years. It just needs Baxi to admit it and put out a general warning. I think a warning is necessary because it's a fire-bomb waiting to happen.

I rang Baxi tech support and really pressed them about the excess heat and they didn't have a clue. There was not one suggestion or offer of help or any interest at all. I told him about the low working pressure and he said this would seriously affect the performance of the gas valve. Rubbish!! Actually this is where the zero governor is a pain - as soon as the flow restriction of the ceramic was lowered (when the ceramic lifted off its seat) the flow rate through the fan rose exponentially and the valve just increased the flow of gas to match resulting in an inferno in the combustion chamber. If that is not a design fault then I don't know what is...

So if you service the Baxi 100 HE range (or any boiler that uses that burner) I suggest it's replace every third service.
 
I thought it was the gas valve to start with. I was lucky to see the ceramic move as the thing overheated. It was a one in a million chance that I saw the movement. It took me a couple of months of contemplation after that before I realised the implications and could formulated a coherent explanation.

The difficulty is that after a boiler has overheated and switched off, the glued-in ceramic cools off, solidifies and looks perfectly OK. So even in a bad overheating incident there would be no reason to suspect the burner. I have not had so much experience with the older burner with the cloth-like, or fibrous element, but the one I have seen had very poor seals around the edge where it was bedded into the pressed steel burner base.

In my opinion this is manufacturing and design fault. After a fair bit of investigation I realised there is no national authoritative body to report issues like this. The Gas Safe Register can't help, and as many of their staff where employed by the large boiler manufacturers, one could be forgiven to think they are there to suppress any bad press about their old employers products. The Fire Brigade can't help and the HSE want someone to die before they will get out of bed. After reporting it to my MP it did get as far as the Baxi's CEO but off course he said it is fine, and my MP believed him!

I would love to get hold of a set of pictures of melted heat exchangers from this range of boilers so that I could re-start my campaign to force Baxi to start a national repair process. There was a picture in the September Gas Engineer but despite numerous attempts at contacting the contributor, he would not respond.

I would be interested to know how you get on. Could you provide the boiler CG number please?

wish i had seen this post earlier - but did get there in the end put my photos on the thread baxi 100he combi
 
The only way of stopping thermal runaway of those BAXI fireboxes would be by restricting the gas flow by gas isolator/service cock (partially closed) before the boiler (or fitting a suitable in-line orifice), so it can't maintain 1:1 air/gas ratio on high outputs (above rated power)...
I would certainly not recommend running the boiler with a defective burner. A fix like this could result in boiler meltdown just as much as with the fault left unaddressed.

...As to me, this is major design flaw: why the governor allows more gas in than the rated boiler input? ...
The regulator is a 1:1. This means that it adjusts the gas flow to match the air flow through the fan. The effect is that the fan speed controls the flow of combustion mixture flow. The heat input is therefore controlled directly by adjusting the fan speed. If the burner ceramic face lifts and creates a large gap, the fan is then allowed to over-speed due to lack of back-pressure. The gas flow rate follows, and as said before, furnace-like quantities of combustion mixture enter the combustion chamber. No wonder it overheats and melts...

It you read my report you will see that there is every chance that no one will ever realise that the boiler has overheated because of the way in which the fault shows itself. I would imagine Baxi realise this and don't admit to the fault and steer clear of discussing it. That's why I suspect that no insurance claims have been made.
 

Attachments

  • baxi 5.jpg
    baxi 5.jpg
    90.9 KB · Views: 42
  • baxi 4.jpg
    baxi 4.jpg
    91.6 KB · Views: 42
  • baxi 3.jpg
    baxi 3.jpg
    95.5 KB · Views: 43
  • baxi 1.jpg
    baxi 1.jpg
    92.2 KB · Views: 42
as this post states only noticed the burner panel lifting on full hw max gas rate as stated by thread starter one to watch for - this customer was lucky from what the thread says the heat ex could melt .
 
These are brilliant photos. Thanks to Buckley Plumb. I wish we could find more examples and then I would be willing to go back to my MP. In fact I may just do that anyway. I know there are other boilers out there that are much worse. This is not too different from the one I encountered in 2010 which finally made me think about what was happening. I mean, would you look at that burner and think there was anything wrong with it? Probably not. Clearly a really hot flame has come from, presumably, the burner. But then there is the dilemma of how could that happen? Once it is explained that the glue of the ceramic gives way and allows the ceramic to lift and create a big gap around its edge, then the downwards flame becomes a realistic proposition.

The Sherlock Holmes - type mystery is then put in place by the ceramic settling back into the burner base making it look perfectly OK. And once it has cooled the ceramic will be secure and not give any clues that it is faulty. The one I saw in 2008 had a totally melted heat exchanger but the burner looked just the same as above. I didn't take a photo ... aarrrgggh!

I actually think this boiler would work perfectly well if this fault did not exist. Ok, the trap would be a pain; but there would be none of the lock-out or overheating issues. I have replaced burners on a couple of these and they are running fine. I have a note when the third anniversary is due, and the customers are happy to pay for new burners as I have recommended.

Actually I think BPs customer was lucky because this boiler could easily kill. It could start a fire as easily as can be. There may already have been incidents. A full-blown fire would destroy the boiler though and effectively destroy the evidence that shows how the fire started. Baxi are fully aware of this issue now because I have told them. They know however that any fire would destroy the evidence that would otherwise condemn the boiler. The only way we can make the authorities take notice is to find more pictures and installers who would be willing to tell their story.
 
Right, now we've non verified gsr's joining in on this. I've been uneasy about where this thread was and letting it ride but enough's enough.

Moving to the private forum.
 
I have re system boiler at the new house , boiler does not responded to thermostat knob and only cuts out on the high limit ..... thermistor reads 2.6 k ohms
high limit stats are on 0.5 ohms .... Burner pressure is 18.5 mbar
any one experienced this ?
 
I have re system boiler at the new house , boiler does not responded to thermostat knob and only cuts out on the high limit ..... thermistor reads 2.6 k ohms
high limit stats are on 0.5 ohms .... Burner pressure is 18.5 mbar
any one experienced this ?

Have you checked the inner door seals? The red seal crumbles away and the fan limit stat trips, throwing the over heat light. The boiler might not actually be getting that hot for the control knob to work.
 
Have you checked the inner door seals? The red seal crumbles away and the fan limit stat trips, throwing the over heat light. The boiler might not actually be getting that hot for the control knob to work.
in worse case the burner can lift causing melt down
 
I have cheked all burner seals and they are good . CO is 15ppm and ratio 0,0002