Hi,
I did ask this question a few days ago, but I wasn't quite sure from the answers if what I was doing was ok. So I'm asking again with a specific question. This is sketch of the branch pipe I am proposing to fit. soil.pngThis is a 40mm bath waste pipe.The total fall is much higher than the building regs H1 document 18-90mm/m. The length of the horizontal run is around 2.5 m, and will be 44mm/m gradient.
Is fitting the vertical section of 40mm pipe ok ? I was going to fit a hepvo trap/valve on the bath waste so I think it should satisfy the requirements in H1 ?
Thanks
 
Is the only a bath going into it where's the basin going ??
 
Not sure why fitting a HepvO trap will help with your fall? Looking at your drawing you have a lot more fall that 90mm.
Is there something I'm missing?
 
The horizontal sections of the pipe require the fall.
Each section of horizontal pipe requires its own fall.
You don't include any vertical sections of pipes fall.
 
Not sure why fitting a HepvO trap will help with your fall?
The building regs H1 quote the fall figures for an unvented branch pipe, as I understand it with a greater fall causes a higher water flow which means there's maybe enough negative pressure to empty the waste trap. If you vent a waste pipe then you can have a greater fall. The hepvo being dry will allow the negative pressure to be released, and then seal the waste again. Am I misunderstanding ?

Looking at your drawing you have a lot more fall that 90mm.
Is there something I'm missing?
The fall on the horizontal section of the branch is 44mm/m, and I set the length of the vertical section so that the horizontal section fall is about right. The total fall is definitely higher than 90mm/m, but venting the branch should then prevent problems ?
 
Last edited:
The horizontal sections of the pipe require the fall.
Each section of horizontal pipe requires its own fall.
You don't include any vertical sections of pipes fall.

Ok, that's the bit the H1 regs do not mention anywhere that I can see :) I did think if you had a long vertical fall there is a risk the trap could have it's water seal pulled out by the pressure caused by the water falling down the vertical pipe section ?
 
The fall on the horizontal section of the branch is 44mm/m, and I set the length of the vertical section so that the horizontal section fall is about right. The total fall is definitely higher than 90mm/m, but venting the branch should then prevent problems ?
Its the first time you have mentioned an unvented soil pipe.
with an unvented soil pipe I would be more worried about gas pressure build up than too much water flow to drain 3" bath trap.
 
What I didn't mention was that you include all horizontal and vertical sections in total length of the waste pipe.

The waste pipe is measured from the trap at the fixture to the connection to the stack.
If you exceed the maximum length of the waste pipe you will either have to vent the waste pipe, increase the diameter of the waste pipe, or both.

The case of the long vertical fall is therefore answered
 
Its the first time you have mentioned an unvented soil pipe.
with an unvented soil pipe I would be more worried about gas pressure build up than too much water flow to drain 3" bath trap.
I didn't think I mentioned an unvented soil pipe. The soil pipe is a standard 110mm pvc with the top end open to atmosphere. I was talking about venting the branch pipe if required ?
 
What I didn't mention was that you include all horizontal and vertical sections in total length of the waste pipe.

The waste pipe is measured from the trap at the fixture to the connection to the stack.
If you exceed the maximum length of the waste pipe you will either have to vent the waste pipe, increase the diameter of the waste pipe, or both.

The case of the long vertical fall is therefore answered

I think you have answered my question :) The total length from trap to soil pipe is less than the 3m max regs figure for a 40mm pipe. And although there are vertical sections, I will meet the specified fall figures for the horizontal sections of the branch, so all is well.
I may still use the hepvo as it neatly fits under the bath without having to put a conventional 3" seal p/bottle trap partly through the floorboards as it's congested under there with other pipe work.

Thanks
 