hi guys. I’ve changed a heat ex gasket on a 24ri today and it was the 1st one I’ve done. For the life of me I couldn’t seem to get the whole thing flat. I put the analyser round it to check for anything passing and didn’t pick anything up. My colleagues reckoned it looked sound but I’m after another opinion if you don’t mind. I’ll attach a pic.

0BBD48C5-7C43-4FD5-879E-BC5535C3795A.jpeg


CF050AAB-D925-4FCD-B7B6-62ECEC24A8DC.jpeg
 
locked in fully at the back?

plate flat?
 
That’s the burner down. And the gasket sat down nice. When I put the plate on and clipped it in at the back it just didn’t seem to sit brilliantly.

212BC76C-3CAF-4BAA-92D2-9FBB61FE9CB2.jpeg
 
If you have located the seal plate tongue into the locating slot & then tightened it down in the front then you are all good.

I always change the electrodes at the same time unless i know that they have not been in long.

Simple design but sometimes can be a bit awkward with the new gasket & then other times it just comes together perfectly first time.

You get used to them after a while,

Cheers,

Andy
 
If you have located the seal plate tongue into the locating slot & then tightened it down in the front then you are all good.

I always change the electrodes at the same time unless i know that they have not been in long.

Simple design but sometimes can be a bit awkward with the new gasket & then other times it just comes together perfectly first time.

You get used to them after a while,

Cheers,

Andy
Seal plate tongue slot?? Sorry for my ignorance mate.
I made sure the burner was sat down properly and that the new gasket was sat down flat whilst also slotting the gasket holes over the 2 pins at the back. I then put the plate in at an angle so that it sat under the housing at the back which brought the plate bang inline with the front rod which houses the nut. I couldn’t work out what more I could do to be honest. I did have a fight trying to get the fan back in though.
Also how do you guys check the gas connection where the circlip holds it on to the valve? I ldf it whilst the boiler was fired.
 
looks fine to me
 

Reply to Worcester heat exchanger gasket? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Locked
hello, I have a Worcester greenstart 440 Cdi combi boiler feeding a wet underfloor to my whole house. There’s one manifold upstairs and...
Replies
20
Views
20K
  • Locked
Hello All My Boiler is dropping pressure and the hot taps are running lukewarm. Pressure was never great..3 floors up so only ever just over 1...
Replies
2
Views
3K
Dotty
D
  • Locked
Was changing 3 rad valves on a combi in a flat. Create a vaccuum to avoid drain down, changed the valves, re-filled and then when I turned off the...
Replies
6
Views
105
M
  • Locked
Grr… second time at this post after computer wiped the first one! Right, I’ve just moved into a new house – the house is not new (30y/o) but it...
Replies
9
Views
1K
D
  • Locked
Hi, Hoping to get some help with oldish boiler - Worcester 24i RSF. Over the last few years the pressure on the DHW has dropped by about half...
Replies
12
Views
4K
Ermintrude
E
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock