Yes, the table gives (presumably) burner output, the only assumption that will marginally affect the boiler output is its efficiency so 85% to 92% should cover it, the calculation for pressure is universally used, ie flow is prop to the sq.root of pressure, I should have shown that as ^0.5 and not ^2, but I did use ^0.5 in the calculation.

Can't really comment on that by pass except to suggest finding out exactly where the connections are teed in.
Thank you for the calculations they are very handy.

I am totally stumped over the whole system 😂😂😂 but have quite a bit more knowledge now thanks to you.
 
This Laundry Manifold/TMV is a mystery to me as all the indications are that the return temperature to the boiler is the mixed flow temperature but havn't figured out if this is thermodynamically possible.
You might please take the (4) temperatures where indicated and also take the return temperature to the boiler; at the boiler.

1658598991413.png
 

Attachments

  • UFH Laundry Rev2.jpeg
    UFH Laundry Rev2.jpeg
    709 KB · Views: 7
  • Watts IsoTherm UFH TMV.pdf
    307.5 KB · Views: 9
Last edited:
This Laundry Manifold/TMV is a mystery to me as all the indications are that the return temperature to the boiler is the mixed flow temperature but havn't figured out if this is thermodynamically possible.
You might please take the (4) temperatures where indicated and also take the return temperature to the boiler; at the boiler.

View attachment 76807
Boiler set point 60
Boiler flow temp 72
Boiler return 59

Ufh at points 2 72 into mixing valve 50 going into pump.

Point 4 45 degrees
Point 8 57 degrees

Wow temps are all over the place. Return is high into boiler as that manual bypass is open.

I have attached a graph of the laundry manifold with boiler flor and return temps taken when boiler was set at 35kw. (Blue is boiler firing flow , Red is pump only pumping)
995F0AFB-0986-4069-BFE1-306663E3A7DD.jpeg
5BB9AC51-5136-4739-9FD0-9746B35D0A5C.jpeg
 
Sorry for confusing you, its the temperatures at 1,2,3&4 in this attachment I would like.
 

Attachments

  • UFH Laundry Rev2.jpeg
    UFH Laundry Rev2.jpeg
    709 KB · Views: 6
Have added another one below, point 5, so measurements at points 1,2,3,4,5. (thanks for your patience)
 

Attachments

  • UFH Laundry Rev2.jpeg
    UFH Laundry Rev2.jpeg
    711 KB · Views: 10
Yes, it's working as I thought it might, apart from temp 1 at 60C which should be the same as the boiler flow at 76.5C or vica versa. The TMV is controlling (first mixing) the temp at 48C = temp 5, this is then (second) mixing with the manifold return of 34C to give a final mixed manifold temperature of 38C, there is only a dT of 4C across the loops so do your calc, LPM*60*dT/860, to give the loop output, kw.
The TMV mixed flow temp of 48C is returning to the boiler which is very good from a balanced corrosion and efficiency point of view, obviously if you require the manifold flow temp of 38c increased then you have to increase the TMV setting.

Its quite a clever control system IMO especially for a oil fired system as it obviates the need for recirculation if the manifold return was returned to the boiler.
 
Out
Yes, it's working as I thought it might, apart from temp 1 at 60C which should be the same as the boiler flow at 76.5C or vica versa. The TMV is controlling (first mixing) the temp at 48C = temp 5, this is then (second) mixing with the manifold return of 34C to give a final mixed manifold temperature of 38C, there is only a dT of 4C across the loops so do your calc, LPM*60*dT/860, to give the loop output, kw.
The TMV mixed flow temp of 48C is returning to the boiler which is very good from a balanced corrosion and efficiency point of view, obviously if you require the manifold flow temp of 38c increased then you have to increase the TMV setting.

Its quite a clever control system IMO especially for a oil fired system as it obviates the need for recirculation if the manifold return was returned to the boiler.
Yes I can’t work out why the flow temp at 1 isn’t the same as the boiler. Output of 4.1kw.

It’s a shame the kitchen manifold doesn’t run like this. I ran it after this manifold and could not even get the flow temp out of boiler up to 55, but yet this got to 76.5 at boiler

Another thing I noticed today, if you reduce the pressure on the pump while radiators are calling for heat the flow temp rises and so does the return temp.

But if you reduce the pump pressure when the UFH is calling the flow temp rises and the return temp drops.
 
Last edited:
Heatloss on pipework?
 
A headscratcher Shaun, the return from the manifold to the boiler is a measured 46C (but is possibly 47C/48C) and its 46.3C measured at the boiler so very little loss in this pipework. The heat loss based on 76.5C/60C and a boiler flow of ~ 4.2LPM = loss of 4.57kw, no way IMO. (Boiler flow 76.C measured at the boiler, 60C measured at the manifold)
 

Attachments

  • UFH Laundry Rev3.jpg
    UFH Laundry Rev3.jpg
    716.8 KB · Views: 7
Last edited:
Yes possibly. should the pump be set to flow rate instead of constant pressure?

Problem with setting it as flow is that’s ok if you have no controls and the load is matched eg your Heatloss is the same as your rads/ufh

But as you have multiple zones and on off controls I would leave it on pressure

The other way to do it is temp difference but you require a sensor if the pump is capable
 
Op can you go round and when the system is on measure all of the flows and see if there’s any difference in temp etc ?
 
A headscratcher Shaun, the return from the manifold to the boiler is a measured 46C (but is possibly 47C/48C) and its 46.3C measured at the boiler so very little loss in this pipework. The heat loss based on 76.5C/60C and a boiler flow of ~ 4.2LPM = loss of 4.57kw, no way IMO. (Boiler flow 76.C measured at the boiler, 60C measured at the manifold)
Very confusing, I believe something is happening inside the boiler as the setpoint was 65 degrees but the flow leaving the boiler is high.

Flow gets well above setpoint with laundry UFH & Rads

Flow does not reach set point for Kitchen ufh manifold.
 
If you press the right arrow on the pump should show the flow rate
 
I get 21kw providing your lpm is correct

Also ufh is a dt 7 not 12

Very confusing, I believe something is happening inside the boiler as the setpoint was 65 degrees but the flow leaving the boiler is high.

Flow gets well above setpoint with laundry UFH & Rads

Flow does not reach set point for Kitchen ufh manifold.
Can't show calcs just now but 60C does tally with manifold flow and temps, try and measure that 76.5C boiler temp as far away on the pipe as you can but before any T off to anywhere, the only way that it's a tue temperature is if the boiler is cycling rapidly but with the off time way longer than the on time, the temp will then certainly reach very high temps especially if no pump overrun installed. The boiler circ rate at 4.1kw manifold requirement will mean/should result in a lot of cycling especially with a boiler flow rate of less than 5LPM.
 
Can't show calcs just now but 60C does tally with manifold flow and temps, try and measure that 76.5C boiler temp as far away on the pipe as you can but before any T off to anywhere, the only way that it's a tue temperature is if the boiler is cycling rapidly but with the off time way longer than the on time, the temp will then certainly reach very high temps especially if no pump overrun installed. The boiler circ rate at 4.1kw manifold requirement will mean/should result in a lot of cycling especially with a boiler flow rate of less than 5LPM.
Ok, I’ll move the thermostat to the flow pipe before it tees of into the valves for UFH manifolds. Thank you.
 
Can't show calcs just now but 60C does tally with manifold flow and temps, try and measure that 76.5C boiler temp as far away on the pipe as you can but before any T off to anywhere, the only way that it's a tue temperature is if the boiler is cycling rapidly but with the off time way longer than the on time, the temp will then certainly reach very high temps especially if no pump overrun installed. The boiler circ rate at 4.1kw manifold requirement will mean/should result in a lot of cycling especially with a boiler flow rate of less than 5LPM.
So I ran the boiler and watch, flow directly out the back of the boiler 75 degrees on 2 different thermometers, temperature before 2 way valve for UFH manifold was 60 degrees.

This could possible explain the short cycling and the boiler re firing again when the flow water is still reading 66 degrees at the boiler.

I also ran the same experiment with the Kitchen manifold, flow temperature directly out of the boiler 54 degrees, flow temperature before 2 way valve for ufh manifold was 54 degrees. Never reached boiler setpoint.
 
Last edited:
Boiler not cutting out on kitchen manifold probably because heat demand greater than boiler output?

When boiler cycles on laundry manifold the circ pump should continue to run continuously even when the burner cuts out and should only stop when room stat shuts the boiler down, check this out, also monitor boiler temp while burner off and note the temperature that it cuts in at again, should normally be a 10 deg hysteresis before cut in, my 20kw Firebird has 10/12 deg.
 
Boiler not cutting out on kitchen manifold probably because heat demand greater than boiler output?

When boiler cycles on laundry manifold the circ pump should continue to run continuously even when the burner cuts out and should only stop when room stat shuts the boiler down, check this out, also monitor boiler temp while burner off and note the temperature that it cuts in at again, should normally be a 10 deg hysteresis before cut in, my 20kw Firebird has 10/12 deg.
Yes circ pump continues when boiler cuts out and stops when room starts reaches temperature.

When the boiler is off the temp on return rises and flow drops and boiler cuts in again when flow temp is 66/67 degrees. Return temp is 57 degrees.
 
Definitely not low temperature corrosion!

What do Firrebird say? Ask them what they think of the nozzle selection and especially their thoughts on the 14 bar pump pressure.

Saw damage similar to this but not as bad where the circulation was wrong way round and had been for 8 years, boiler used to trip occasionally on its hi limit pstat.
 
Last edited:
Definitely not low temperature corrosion!

What do Firrebird say? Ask them what they think of the nozzle selection and especially their thoughts on the 14 bar pump pressure.

Saw damage similar to this but not as bad where the circulation was wrong way round and had been for 8 years, boiler used to trip occasionally on its hi limit pstat.
I’m trying to get some answers out of firebird now to see what they have to say. Will let you know
 
I would say overfired
 
I'm not surprised your having difficulty getting answers from firebird.
In general I've found them to be evasive often useless.
Plus the minute boiler out of warranty they totally refuse to even talk to you.
Plus unfortunately you have a installer who to put it politely ain't up to speed.
 
H
Definitely not low temperature corrosion!

What do Firrebird say? Ask them what they think of the nozzle selection and especially their thoughts on the 14 bar pump pressure.

Saw damage similar to this but not as bad where the circulation was wrong way round and had been for 8 years, boiler used to trip occasionally on its hi limit pstat
Have tried to get some answers from Firebird but no one is interested to answer questions.
 

Reply to What size boiler needed in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi. I need a new toilet supply line but don’t know the size type of the fitting at the shut off valve. It is not 3/8 compression. It is a plastic nut about the same size as the one going into the cistern but has a different thread. Attached is a photo. Can you advise. Thanks.
Replies
2
Views
192
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
215
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
266
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
348
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...