Pauld1962

DiddlyP
Messages
9
Called to a customer today and the system boiler keeps repressurising on its own ... After I dropped out all the pressure I watched as it refilled ... The filling loop was disconnected at the time ... Customer reports that it's never done it before ... The only way I could stop it was to turn off the cold mains ... !! ... Any help appreciated ..
 
Combi boiler ?
 
It's an old system boiler Vaillant thermocompact vu 282/1e ... Unvented cylinder ... Is there a test for split coil and what causes it ... They use the immersion most of the time as solar power is available ..
 
Drain & valve off cylinder coil in that way they can still use the immersion or Solar for domestic hot water.
The heating system pressure should stop rising. If so it is the coil & you will have to order a new cylinder.
 
I isolated the F&R at the boiler at 1.5bar and it held .. Once the return was opened the pressure rose immediately and water meter was turning over .

Probably cylinder coil gone then.
Is it a copper unvented cylinder, or stainless steel?
If you are not G3 qualified, just be aware if no isolating valve on mains supply to unvented cylinder, then only install one BEFORE the combination valve. (Between the combination valve and cylinder must not have any valve)
 

Reply to Unvented heating system, unusual boiler fault in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator pipes during the strip out. Not the end of the world as damages happens. I am responsible builder and paying my bills and to repair the damages if...
Replies
2
Views
90
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
227
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
248
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
397
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock