bassmonster

Plumbers Arms member
Plumber
Gas Engineer
Messages
562
hey all,
I'm just ticking off the boxes in my completed tasks folder for my ACS and for some reason my mind has gone completely blank.

Ok, so in all my 12 jobs, i have to carry measure operating pressure on the appliance. correct me if i'm wrong, you cannot carry out operating pressure if the boiler has a zero governor ? is there any other way of measuring the operating pressure on a boiler with a zero governor like through some calculation with the meter?
 
Operating pressure/burner pressure cannot be taken on zero governed boiler. This is when a gas rate is required.
 
I suspect the OP means the working pressure of the appliance rather than the
burner pressure.

The working pressure is the pressure delivered at the appliance, this would usually
be taken from a test point very near to the appliance or from the gas valve P1 point
on the valve.
 
Irrelevant on a zero governor as there is a vacuum in the pipework and you will never get a correct measurement.

If it's gas rated correctly and the combustion is okay, the it's fine.
 
Irrelevant on a zero governor as there is a vacuum in the pipework and you will never get a correct measurement.

If it's gas rated correctly and the combustion is okay, the it's fine.
Disagree.
You can still check working pressure on a zero governor and I still do at times. You should still get around say 16mb minimum on a greenstar at P1 for example.
 
Disagree.
You can still check working pressure on a zero governor and I still do at times. You should still get around say 16mb minimum on a greenstar at P1 for example.

Hes talking about burner pressure.

you should always check working pressure at p1!
 
Disagree.
You can still check working pressure on a zero governor and I still do at times. You should still get around say 16mb minimum on a greenstar at P1 for example.

You can check at the test point but the reading is almost meaningless with the appliance running.
 
so how do you know you have less than a 1 mb drop on your pipework?working inlet pressure should be measured and a zero govenor will have no effect
 
You can't. Because gas isn't just travelling down the pipe under positive pressure, it's being sucked through the pipe under negative pressure. Why do you think the manufacturers quote such low book figures for inlet reading?

Ideal quote as low as 14mb at the test nipple.
 
You can't. Because gas isn't just travelling down the pipe under positive pressure, it's being sucked through the pipe under negative pressure. Why do you think the manufacturers quote such low book figures for inlet reading?

Ideal quote as low as 14mb at the test nipple.

you cant be sure you have 1mb drop without a fitted test point really. but you can check that the pipework has no more than a 2.5mb drop from the meter which would def indicate with most appliances the gas pipework is undersized and a risk to other appliances.

the min working pressures stated by the manufacturer is only supposed to be seen when gas supply pressures are low and not badly sized pipework. Ideal are stating that the boiler works safely at that pressure, with a consideration of16mb meter working pressure at "peak" times being thought about.
 
Thank you for the replies.

My portfolio states that it's "operating pressure" which i need to record. does that mean the term "working pressure" is the same thing?

when connecting the gauge to the p1 test point, would i record the pressure whilst the appliance is running or off?

am i correct in thinking that even a zero governor gas valve will have a p1 test point?
 
The p1 point mentioned is the gas inlet test point. It will give you the working inlet pressure at the gas valve. The operating or burner pressure will be zero more or less. In the box for operating pressure either put the gas rate or write zero, zero guvna.

Yes the gas valve will prob have both inlet and burner test points.
 
The p1 point mentioned is the gas inlet test point. It will give you the working inlet pressure at the gas valve. The operating or burner pressure will be zero more or less. In the box for operating pressure either put the gas rate or write zero, zero guvna.

Yes the gas valve will prob have both inlet and burner test points.

why did i not think of that..?:thinking::thinking::thinking:

thanks mate.....
 
In your practical assessments you will most likely be asked to check the working pressure on a zero governor burner, to check that when you get the zero reading you understand what type of control you are dealing with.
 
New posts
Status
Not open for further replies.

Reply to Trainee gas questions in this thread ONLY please in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock