Dear All

New member here, coming looking for help. A few weeks ago I had work carried out by a British Gas Homecare service technician. It required a drain and refill of the system, and as he left, he advised my I would need to bleed all the radiators, at some point, given a few days, when everything had settled down. I followed this advice, but got no gurgling or spitting from any of them, and just nice clean water coming out, so I felt happy about that.

Since the work was carried out though, I have been having awful problems with overpressure. Not that my boiler tells me that easily, no light codes, as far as I can see, but it regularly fails to start, and if I catch it trying, it just clicks a few times, and then gives up. When I check the pressure gauge, which is in the loft, I see significant overpressure, such that I need to bleed around a gallon and a half of water out of the system to bring it back down again, which I do at an easy to access radiator.

Where the gauge is there is a red coloured pressure vessel, and leading to that is what I take to be a mains water feed, with two taps in a line, I assume for double security. Both of these taps are definitely in the off position, because if I turn them both on, I hear water flowing, and the gauge goes up, which is what I would normally do to top the system off, if ever it's needed, which on occasion, it has been in the past.

As it stands though, that is never going to be required again, because since the technician was here, in order to keep my hot water and heating system going, I have had to drain gallons and gallons of water out of the system, around a gallon and a half every few days.

My thought is there is another feed location, somewhere nearer the boiler, which he utilised to recharge the system, and he has left that in the on position, or partially on. Before I remove all the woodwork surrounding and covering the pipes near the boiler, is this a possibility, and should it be easy to identify. It's quite the task to get all this off, and I don't want to waste my time if there is no such alternate feed.

I'm a complete novice when it comes to boilers and heating, but I'm not helpless in terms of general mechanical ability, and DIY, so I'm hopeful that if my thoughts are correct, I will be able to spot another valve or similar, and crank it down.

If it helps the boiler is Potterton Precision, and has been operating for around 10 years, with regular service and periodic repairs from British Gas Homecare. They tell me that my system is an S plan heating system, whatever that means, again if that helps.

If you need more information, so that I can be helped, do please let me know, and I will try to find out.

I'll not go into detail as to why I can't just log a recall with Homecare, but please take my word for it, that at this moment, I cannot. If you think that's definitely what I should do, I will explain why.

Thanks in advance for any help you can offer.

Cheers

Sutty
 
What type of hot water cylinder do you have? (Is it a pressurised 'unvented' type or a low pressure 'vented' type fed from a tank in the roof.
 
As I said, I'm a beginner, so I'm not certain, however, I could guess that it's sealed, because our hot water pressure is dependent on the cold water pressure. If the cold water has low pressure, due to some network fault, or similar, the hot water is equally affected.

It is the pressure in the radiators though that the gauge shows, and I can correct it for a couple of days or so, by bleeding a lot of water from the radiators, and then my boiler will start. Not sure how that relates to the hot water, but hopefully what I've described will point to a sealed hot water tank, if it does help. Let me know if it doesn't, and maybe I could take photos?
 
There should be a flexible section of pipe (hose with a metal braided covering) between the two isolation valves you use to fill the system. With the isolation valves 'off' this should be disconnected during normal use because the valves only need to pass a very small amount of water to create the problems you are describing. One end of the hose will have lugs so you don't need tools to disconnect it. If one of the valves is passing you will probably be able to see water slowly dripping out.

Another possibility, but much less likely, is the heat exchanger in your hot water tank leaking so domestic hot water is getting into the heating circuit. You might be able to prove this for yourself as follows. Wait until the CH pressure has risen. Take a photo of the pressure gauge. Turn off the valve that supplies cold water to to the cylinder. Open the lowest hot tap in the house and let it run until it stops. (You'll have to waste a couple of quid's worth of hot water, sorry) Now monitor the CH pressure over several hours to see if it starts falling.

A professional (G3 qualified) plumber might isolate and then pressure test the heat exchanger or put fluorescent dye in the CH water to see if it emerged in the domestic hot water but this these are not tests you should attempt yourself.
 
There should be a flexible section of pipe (hose with a metal braided covering) between the two isolation valves you use to fill the system. With the isolation valves 'off' this should be disconnected during normal use because the valves only need to pass a very small amount of water to create the problems you are describing. One end of the hose will have lugs so you don't need tools to disconnect it. If one of the valves is passing you will probably be able to see water slowly dripping out.

Another possibility, but much less likely, is the heat exchanger in your hot water tank leaking so domestic hot water is getting into the heating circuit. You might be able to prove this for yourself as follows. Wait until the CH pressure has risen. Take a photo of the pressure gauge. Turn off the valve that supplies cold water to to the cylinder. Open the lowest hot tap in the house and let it run until it stops. (You'll have to waste a couple of quid's worth of hot water, sorry) Now monitor the CH pressure over several hours to see if it starts falling.

A professional (G3 qualified) plumber might isolate and then pressure test the heat exchanger or put fluorescent dye in the CH water to see if it emerged in the domestic hot water but this these are not tests you should attempt yourself.
Okay, from what you describe, it would seem there is no other place it can be being filled, without a fault, so no point looking. I can perform the tests you describe, and will do so. There is a braided hose, as you described.

The technician described something to me, whilst here, but I don't recall it properly, along the lines of, you have a such and such system, and I love working on systems like this, because they are so easy to refill, and I suppose that's probably what got me to thinking along the lines of an alternate fill option.

I'll try to get more details for tomorrow, but I need to get some sleep now. Thank you for the advice so far.

Regards

Sutty
 
It's already significantly over pressure, after only 16 hours, having bled it down at around 7PM yesterday, and with it being 11AM when I checked it a short while ago. The boiler is still running, but it's close to where it will stop, judging by the position of the gauge.

Not clear how it can get to this state, if only one isolation valve is faulty. Wouldn't both have to be? Anyway, I'll take a look after lunch, to see if there is a leak there, by disconnecting, as instructed.

If not, I will restore that, and then look to drain the system down, until empty. Will this present any difficulty refilling, with it being sealed? How does that work if the low tap is now off again, and the tank is now full of air, when I turn back on the feed to the tank? I won't do that until I hear from someone that this will go okay.
 
Not clear how it can get to this state, if only one isolation valve is faulty. Wouldn't both have to be? Anyway, I'll take a look after lunch, to see if there is a leak there, by disconnecting, as instructed.

After a bit of use, those valves may well 'pass' to some (small) extent but that can be all that's needed to cause over-pressuring. That's why you a have a piece of flexible hose that you can disconnect at one end. If you read the instruction book for your system it will tell you to disconnect it after topping up.

If not, I will restore that, and then look to drain the system down, until empty.

Whoa there cowboy! I did not say 'drain the system down' I said open the lowest hot tap and let it run dry with the inlet to the hot cylinder isolated, which might require a couple of gallons of run off. (On reflection, my 'couple of quid' of hot water was an overstatement.) This will leave the cylinder full of water but at a pressure below that of the heating circuit. When you've finished make sure the hot tap is closed and gently open the valve supplying cold to the cylinder again. Expect a bit of sputtering when you first draw hot water after doing this so open the tap carefully.

If you don't understand what you are doing and why, please call a plumber.
 
Last edited:
Those valves quite often 'pass' to some (small) extent but that can be all that's needed to cause overpressuring. That's why you a have a piece of flexible hose that you can disconnect at one end. If you read the instruction book for your system it will tell you to disconnect it after topping up.



Whoa there cowboy! I did not say 'drain the system down' I said open the lowest hot tap and let it run dry with the inlet to the hot cylinder isolated, which might require a couple of gallons of run off. (On reflection, my 'couple of quid' of hot water was an overstatement.) This will leave the cylinder full of water but at a pressure below that of the heating circuit. When you've finished make sure the hot tap is closed and gently open the valve supplying cold to the cylinder again.

If you don't understand what you are doing and why, please call a plumber.
Lol, yes, my assumption was that if the HW fill valve was closed off, and the low tap opened, and it was Ā£2 of hot water, that would be emptying the whole tank. As for calling a plumber, yes, that would be best, but, for the record, the reason I'm loathed to do so is that my mother just passed away, and this was her account with BG Homecare. I'm in the process of opening an account for me, and even when done, I have no doubt that a recall across accounts, will prove to be exceedingly difficult to arrange, but it should be a recall, because it has never worked since they left. Even if I can't arrange the recall, I don't want to be paying for Homecare insurance, and then not use it, by involving a different plumber. This, why I'd like to solve this myself, just for now, and just for this one issue. If it proves to be beyond me, so be it.

As for not knowing what I'm doing, that's true, but I can follow instructions, and have mainly understood what you are suggesting, and why, so far, and I'm grateful for the guidance. A small misunderstanding about relieving the HW tank pressure, as opposed to the tank being emptied, given my lack of starting knowledge, is perhaps understandable. Now you've explained, I'm with it.

Thanks again.
 
Update on the link. As you described, lugged, and not overtightened connections. Undid one end, and collected the water. Undid the other end, and removed it, so I could more easily dry and observe any water build up in the socket, rather than in the length of pipe. Zero change, or build up of water occurred, and certainly no drips, at either side. Looked for the HW tank fill isolation valve, and saw none at the bottom of the tank, from where I presume it fills, keeping the water hot at the top, but none to be seen near the tank. Will have to look round tomorrow for that, because the issue is not the valves either side of the link.
 
Update on the link. As you described, lugged, and not overtightened connections. Undid one end, and collected the water. Undid the other end, and removed it, so I could more easily dry and observe any water build up in the socket, rather than in the length of pipe. Zero change, or build up of water occurred, and certainly no drips, at either side.
What had 'zero change'? Has removing the link stopped the pressure buildup in the heating system or not? (I suspect not but I try to avoid assumptions.)

Looked for the HW tank fill isolation valve, and saw none at the bottom of the tank, from where I presume it fills, keeping the water hot at the top, but none to be seen near the tank.
Can you post a photo of the tank and nearby pipework? (Just want to check we really do have an unvented cylinder.) Also, what make and model of boiler do you have?

The inlet to the cylinder will be at the bottom. So will be the flow and return to the heat exchanger. There is usually an expansion vessel, maybe 20 litres in volume and painted white between the isolation valve and the cylinder.
 
What had 'zero change'? Has removing the link stopped the pressure buildup in the heating system or not? (I suspect not but I try to avoid assumptions.)


Can you post a photo of the tank and nearby pipework? (Just want to check we really do have an unvented cylinder.) Also, what make and model of boiler do you have?

The inlet to the cylinder will be at the bottom. So will be the flow and return to the heat exchanger. There is usually an expansion vessel, maybe 20 litres in volume and painted white between the isolation valve and the cylinder.
Nice one, thanks. I meant zero change in the dry status of the now opened ends, after having dried them with tissue, and having waited several minutes. with the link completely removed, waiting for drips, from either side, but both ends remained bone dry. Thanks for checking.

There is a white expansion vessel. It's roughly the same height as the red expansion vessel. I only had a quick look for the valve, but will try harder tomorrow. If I get a moment to nip up tonight, I'll take some shots, but maybe the white expansion vessel is a giveaway for you?
 
As per the title, it is a Potterton Precision boiler, though if you need more, let me know. Sadly I haven't had the time to do anything today, due to family commitments, apart from to bleed it, to make it work. I've also just turned off the hot water, on the controller, so see if that would stop the tank crossover, if that's where it is occurring. I figured, if the heating system isn't putting hot water through the tank, maybe it's less likely to be able to be back filled by the heating system? Dunno, but I'm trying it.

I'll be without hot water in the morning, but I can soon correct that, by putting it on for an hour.

Doing so got me to wondering if there might be other potential crossover points, especially with you telling me that there would not be another fill point, and it got me to thinking about what our hot water does. Maybe this will help you to help me, or not, I'm not sure?

Unusually, judging by every technician/plumber that has ever visited, or any friend that I have mentioned this to, when our hot water is on, whether the central heating is on or not, three of our radiators get hot. They get hot, deliberately so, at the request of my late mother, who always wanted to have the bathroom radiators on with which to dry things, if she needed to. It also afforded us the luxury of being able to heat the bathrooms, even if the CH was off, so they were a little warmer, when having a bath, etc, on an averagely warm day, by simply putting the hot water on.

If not needed, in say the height of summer, when it would simply be wasting money, but we would still need hot water, they were simply turned off with the radiator valves.

So, we have three radiators that come on whether it be hot water or central heating that is on, with the only difference being that if they come on as a result of CH, then they are on with all the others. I have no idea how that works, but for sure, it does exactly that.

Maybe this isn't so odd, but the reactions I get seem to suggest it is, but does this suggest there might be some other potential crossover point, or not?

Thanks again for any help.
 
No pressure increase, in the absence of hot water being on. To me that points to what you said, in terms of pressurised tank water crossing over into the CH circuit, although I still have concerns that I'm not at the bottom of it, what with the system's own peculiarities, of having those three radiators that come on with either the HW, or CH. Of course, I don't understand, so this could be a complete red herring.

I have taken photos, see attached, which may help work out what's going on? This system has been in place for as long as I can remember. Certainly long before my father passed, which was 16 year ago now. Probably some 20 years, probably more, I should think, apart from the boiler, which is just 11 years old.

Flexible link (foreground right) and tank overview.

Link from other direction and overview.jpg


Link in other direction, to red vessel, with pressure gauge on top.

Red vessel and flexible link.jpg


Under white vessel. Some sort of capped controls?

Under white vessel.jpg


Some sort of vent or overflow mechanism, to the right hand side of the picture? Have never observed anything running down it, and it's bone dry right now.

Maybe some sort of overflow mechanism.jpg


Thanks, if you can offer any further help.

Cheers

Sutty
 
No pressure increase, in the absence of hot water being on. To me that points to what you said, in terms of pressurised tank water crossing over into the CH circuit, although I still have concerns that I'm not at the bottom of it, what with the system's own peculiarities, of having those three radiators that come on with either the HW, or CH. Of course, I don't understand, so this could be a complete red herring.
If the pressure rise in the CH stops when you reduce the pressure in the hot water cylinder that tells you that the heat exchanger coil in the cylinder has failed, which usually means that the cylinder will need to be replaced. This is a job that can only be done by a plumber with an 'unvented hot water' qualification, sometimes called a 'G3 ticket'.

Bathroom radiators (particularly towel rails) are often plumbed to be 'always on'. It's unusual to have other radiators configured in this manner but it should be fairly straightforward to have them put onto a controlled zone.

Unvented cylinders usually have a long warranty (25 years+) covering the coil and cylinder. There should be a label showing the maker, model, serial number and date of installation on the tank so you can contact the manufacturer to see what the position is. They probably won't pay for the labour but you may get a free / reduced price cylinder.

You have a lot of underinsulated pipework in what looks like a 'cold' roof space. This means that there is a risk of freezing during the winter if the heating can't be left on. I'd want to have a 'frost stat' up there so the heating turns on You're going to have to get a Homecare or a G3 qualified plumber involved.

An unoccupied house with a faulty heating system needs to have the water shut off at the stopcock and then be fully drained, preferably by a qualified plumber.

I don't know how Homecare handle the death of a customer. Standard practice is for the executor(s) to contact the company and arrange to continue making monthly payments to continue the deceased's cover until probate is obtained and the house, and responsibility for its maintenance, passes to the beneficiaries. Big companies usually have a 'bereavement department' who understand the situation and do their best to help.
 
Thank you for the detailed and considered response. Yes, it would seem that I have no choice now, because that would be far beyond me. Interesting to know that it may be under guarantee. I saw the manufacturers label on the tank, and will see if it is.

As for Homecare, one might hope that they would have a department such as that, expert in such matters, however it would seem not. After having made contact, advising them of the required changes, as a result of the death of Mrs Sutty, I received an email back, saying, thank you very much for notifying us of the changes to your account, Mrs Sutty. I promise you I could not have made it clearer that she had passed away.

Eon, on the other hand, as the energy supplier, were simply fantastic, and dealt with everything in an incredibly professional and sympathetic manner.

I will try to call out Homecare in a few days.

Thanks for your help in properly identifying the issue.
 

Reply to Boiler overpressure with Potterton Precision in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. Itā€™s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
324
Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
498
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
231
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going to dig it up and replace it šŸ˜¬. Question is can I use normal 22mm plumbing push-fit connectors to make the connection as finding 22mm MDPE fittings...
Replies
1
Views
263
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock