cr0ft

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,311
Went to this boiler today to service for the first time and found black spillage marks all over the inside of the outer case (mostly inside the airbox seal area but not all, some are clearly visible outside the seal).

Noticed there is a case screw missing on bottom left so am going to replace that and the airbox seal. Anything else obvious to look at? Combustion analysis readings are all within acceptable limits.

Is this common for these boilers? Never seen it myself before.

IMG_0057.JPG


IMG_0057.JPG


IMG_0057.JPG


IMG_0057.JPG
 
common heat damage, i would say 8-10 years old?
 
If that was spillage it would be black bright (pardon the pun)
 
On closer inspection the case is missing one of the retaining screws on the bottom left (couldn't see it till I came to put it back on, hidden by boxing) and it's not sealing properly onto the air box. Going to replace the case screw and fit a new seal just to be safe, both cheap parts. Cheers all.
 
Watch out for a failed burner gasket (red) at the top of the heat exchanger. Even if the values are fine this could be leaking. There is a recommendation from Worcester to change these periodically, bit like the circular one on Vaillant. Not sure of the interval.
By the time it’s leaking fully you could get total meltdown on the other plastics particularly the fan. (Expensive)
 
Thanks mate :)
 
Yes, 10.3% CO and 0.002 with 125 parts CO on max rate.

Ratio down to 0.0005 with new Case seal so something was going on for sure.
 
these combustion boxes are not sealed anyway look in the 4 corner at the back , anyway probably time to change the read seal judging by the amount of staining there and that IS NOT a normal/common amount of black marks/staining within the worcester ( especially system boiler ) ;) and while your at it i expect the heat exchanger could do with cleaning with constant over gassing , you can tell by measuring the fan pressures if it does , but the gas valve on these constantly change from year to year so need adjusting every service probably . probably see about 600 - 800 of these boilers a year
 
Status
Not open for further replies.

Reply to Spillage on inside of case (Worcester Greenstar 24i System, 2001) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock