Hey guys, I have a shower that is failing to get hot water to it... The pump sounds awful when starting up, almost like its running dry! The connection in the airing looks wrong to me the 15mm pipe in the pic goes up & then down onto the pump in 15mm... Isn't the vent supposed to come off the top & the side outlet go to the pump on these flanges? Obviously I can't tell properly without removing the flange!
 

Attachments

  • image.jpg
    image.jpg
    100.5 KB · Views: 135
Vent should come out the top run 450mm horizontally at a slight rise then vent and feed
Shower should come out the side
 
Surrey flange is shower hot out of side connection & vent with hot to other supplies from the top connection.
Warix flange is the opposite way.
 
I had one recently where the hose was collapsing, causing a restriction and an awfull noise.
 
Theirs a thread from a while back similar to this and it turned out the tube inside had fallen off!! Has it always done it or just started?
 