Hi all.
Wondering if anyone uses one of these on new build 1st fix installs rather than the traditional water pressure test ?
Thanks
 
I assume you mean plastic systems?
Has to be water
I know polypipe call for a water test at 18bar for minimum of 15 min max a hour.
Cannot use air for H&S reasons.
 
Can’t go over 0.5 bar on air also you would need the m18 version as the m12 would struggle
 
Sorry for late reply. Thanks for advice. I know there’s one or two lads on our firm that have them. Always tested with water but sometimes I have to walk from one end of the site to the other for water and thought it would make it easier.
 

Reply to Milwaukee mini compressor. in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Good morning all, Just a quick one, ive recently been asked to fit a new fire in a property, there was one in previously but was removed simply...
Replies
3
Views
270
Hi, Short version: Do frost protection valves trigger when the water in the pipe gets to threshold, or when the air temp drops? Long version...
Replies
3
Views
138
A
Hi, I am trying to fit a replacement tap to a mini-sink that's built in to the top of a toilet. The original tap isn't made any more by the...
Replies
5
Views
829
I'm looking at the above, hoping it will be a good all-purpose tool for repairing our 2 megawatt furnaces. I'm a bit unsure if I need any of the...
Replies
1
Views
436
Evening I'll go straight to it.... Ideal mini combi and non thermostat bath shower mixer. Run the hot tap on the mixer boiler fires water stays...
Replies
2
Views
786
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock