Got it :)
 

Attachments

  • final pic1.JPG
    final pic1.JPG
    146.9 KB · Views: 18
This assumes that all the wiring centre power is coming from the same supply circuit as the boiler.
That is the proper and most likely arrangement.

But if you get issues with an rcd tripping (not MCB) then that would point to them being on different circuits from the consumer unit, which would need to be corrected.
 
I believe i understand this now :)

The black wire which enters to the bottom of the Room STAT/Timer block link is carrying power which is carried over through the link into the red wire leaving the bottom and activates the demand for central heating. Hence the boiler firing constantly.

By removing the link and placing the black wire in the 4th position (counting from the earth as number 1) as soon as the thermostats activate, power travels down the black wire and the demand for central heating fires the boiler.

Is my understanding correct?

Edit correct
 
Terminal (from left) 3 Shaun if terminal 4 is live with link removed?? (post 15).

Sorry just seen instructions yep
 

Reply to Logic Combi ESP1 35 always showing demand for Central heating in the USA area at PlumbersForums.net

Similar plumbing topics

M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
283
MartinPod81
M
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
277
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
444
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
409
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
399

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock