I think auto and 24kw settings are far too high for a 5 rad system, probably better with 10 - 12kw.
Thank you for your reply! Could i please ask is this possible to do on this new boiler? The boiler i had previously was 16 years old but also 24Kw so i did like for like change. Is it possible for me to change the setting from Auto to 10/12kw or do you mean i need to get a different boiler with lower Kw?
 
Change d.00 max setting to 10 (kw) or so.

Also see if d.05 (boiler flow temperature) is settable, it states below that it isnt which seems strange, also note the anti cycling time, d.02.

Amazing that the flow/return temps are 38/36C, boiler firing??.
There is a d setting in some of these boilers where you can control the return temperature, it might be in one of the d codes if selected.

When f23 was flagged what did d.40 & d.41 read?.

1680169742335.png
 
Last edited:
Thank you for your reply! Could i please ask is this possible to do on this new boiler? The boiler i had previously was 16 years old but also 24Kw so i did like for like change. Is it possible for me to change the setting from Auto to 10/12kw or do you mean i need to get a different boiler with lower Kw?
You’re welcome. No, i don’t mean swap the boiler. As above, it’s possible to range the heating side down, and shouldn’t affect the hot water delivery - let’s face it, there’s nothing to lose by trying it. I take it you missed my earlier post regarding the motorised valve?
 
No, i don’t mean swap the boiler. As above, it’s possible to range the heating side down, and shouldn’t affect the hot water delivery - let’s face it, there’s nothing to lose by trying it. I take it you missed my earlier post regarding the motorised valve?
Will defiantly try it! Sorry, regarding motorised valves - both were checked and seem to work ok. Always responded even with previouse old boiler so i asked the gas engeener if i should order new ones as we upgrading the system but he was sure they work well still.
 
Update- Same Fault 23 was on the boiler when I got in, I have closed 4 radiators and restarted the boiler, it only keep working if I open the rest of the radiators one by one after they got hot. Temperature on display keeps going up and down and radiator sign keeps flashing. Gas engineer coming back tomorrow to start again, is there anything else I need to tell him? ( I printed all your previous replies for him).
Thank you!
Irina
F9796675-D3C2-44EC-A534-27256C4C86AB.jpeg
DA7E695F-4556-4F73-9A78-11B484A2545F.jpeg
D676433D-7C75-4473-B2C9-D7EEAF9A8ADC.jpeg
5F80C906-407B-4BAF-9DEF-74B4778E9C7C.jpeg
E80EB11A-6BE1-4CB2-8CED-B2E2F5A8DD5C.jpeg
E09CC87A-70A2-4270-8071-C574499A4247.jpeg
9868E3D3-61F1-48DD-BE36-30CFDA68850C.jpeg
61F1FFB7-C832-451E-860B-563AD3268636.jpeg
341DED74-1E3A-42A6-BFDB-32801227A49C.jpeg
8A691A87-AD5F-447A-9B5B-2F3A73BCC84C.jpeg
 
Check the (downward) vertical pipe from the ABV (automatic balancing valve) is cold/cool with boiler running, it looks as if its set to max (ie closed) index of 0.5, 5M. It looks suspiciously as if its teed in to where the cold feed traditionally is/should be, alongside the Vent, if not a combined vent and cold feed, like mine. Try and see where the cold feed pipe is teed into the system it will be a 15mm pipe coming from the side (bottom) of the F&E tank, also check the obvious, that this tank contains water.
 
Last edited:

Reply to Help with New Vaillant Boiler not staying on in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I have a Worcester Bosch Greenstar 15i condenser boiler which is about 13 years old. There is a separate hot water tank. Recently the fan in the...
Replies
3
Views
201
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
285
MartinPod81
M
Would like some help please as my Drayton Wiser system is a mess. I had 2 TRVs in the lounge, one in the main bedroom, the rest of the house - 6...
Replies
3
Views
456
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Replies
1
Views
336
Hello, We had an extension built seven years ago. Initially the builders' plumber connected the heating to the house system but this didn't work...
Replies
23
Views
832
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock