If its the model I think it is then a bit ambiguous re venting so perhaps its detecting "air" on occasions?

Startup
The pump must not be started until the system has
been filled with liquid and vented. Furthermore, the
required minimum inlet pressure must be available at
the pump inlet. The system cannot be vented through
the pump.
The pump is self-venting and does not require venting
before startup.

In speed III, the pump is set to run on the maximum curve under all operating conditions. See fig. 14.
Quick venting of the pump can be obtained by setting the pump to speed III for a short period.
 
Thanks for all the replies, problem has now been solved by replacing the control box that sits on top of the pump (replaced with one from another Grunfos UPS2 pump). The pump now starts without any issues straight from fire up. Replacing the control box is a very straight forward and simple job. Once the top black cover is removed there are 2 screws which locate the control box to the pump. Once these are removed the control box just pulls off, it connects to the pump via a plug. Replacing is simply a reverse of the above. Only problem now is locating a replacement control box for the pump I canniballised. The Grundfos part number is 98662219. I can't find any reference to this part anywere on the internet or in the Grundfos web site. Anyone any suggestions where I might get a replacement other than from another pump?
 
You won’t they don’t sell it separately
 
Had similar problem ups2 pump ticking/pulsing and not starting. Then after a while (12 mins at the last attempt) it would start and run normally. Meanwhile the boiler (WB FS30cdi) would run, overheat and cut out. This would repeat until the pump started.
Solution:Fitted a new pump,-ups3. Operation now normal. It would appear that the old pump was 11years old so it didn't owe me anything.
HTH.
 
Had similar problem ups2 pump ticking/pulsing and not starting. Then after a while (12 mins at the last attempt) it would start and run normally. Meanwhile the boiler (WB FS30cdi) would run, overheat and cut out. This would repeat until the pump started.
Solution:Fitted a new pump,-ups3. Operation now normal. It would appear that the old pump was 11years old so it didn't owe me anything.
HTH.

Capacitor at fault likely
 

Reply to Grundfos UPS2 15-50/60 circulating pump problem in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
767
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
676
Hi Guys, Got a knackered Grundfos UPS 15-60 130. Have a replacement Grundfos UPS3 15-50/65 130. Is the UPS3 pump head compatible with the UPS...
Replies
1
Views
2K
    • Like
Hi there, I’m hoping someone can help me with this problem please. I’ve searched for similar posts but not found anything helpful! My mum’s...
Replies
12
Views
615
I have an older gas boiler HW heating system with a taco circulator pump for each zone that worked fine last season. When turning it on for the...
Replies
4
Views
477
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock