Flame rectification

Discuss Flame rectification in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Disconnect the probe. Set your multimeter to microamps. Connect the probe to one lead and earth the other lead. Fire up the boiler, you should see 6-9 microamps. If you do its the board, if not it's the probe or a bad earth.
 
Last edited by a moderator:
Please correct me if I'm wrong. If the probe is faulty, the boiler would go into lockout any way right? So turning off the gas wouldn't determine the probe being faulty? Confused. Com
 
What will fry it, the test that croppie mentioned?

no,croppies test is correct, the fact that there could be other factors causing the fault,if any electrical work has been done in the house,and the polarity has been reversed this most commonly shows itself as a flame detection fault ,if you dont test for it and think its the pcb you could get your fingers burnt,what supplies the boiler spur or plug?
 
Also as I said, check you've got a good earth.

20150211_141218.jpg
 
Or interrupt the connection between the probe and the harness with your multimeter.

Some newer boilers will give a readout of the ionisation signal on the board display, some need a stronger signal than Croppie quotes.

Worcester quote 35 micro amps on their new compact, I think they have got that wrong though. I can make one run while its reading 15.
 