Ever since the cylinder return balancing valve has been messed with by my kids it hasn't been hot like before what can I do? (as previously I've been told to leave it fully open )
 

Attachments

  • image.jpg
    image.jpg
    564.4 KB · Views: 17
Didn’t I say 3 full turns closed should do it from fully open ?
 
Do one more turn then
 
Correct see what the temp is like might need 1/2 a turn etc
 
What is the boiler flow temperature set to? and are you allowing it enough time to reheat the cylinder??.
If you feel the return (coil) temperature is it hot/warm or only lukewarm?.
Regarding the return valve, anything more than 1 full turn open from fully shut is quite adequate.
 
What is the boiler flow temperature set to? and are you allowing it enough time to reheat the cylinder??.
If you feel the return (coil) temperature is it hot/warm or only lukewarm?.
Regarding the return valve, anything more than 1 full turn open from fully shut is quite adequate.
Hi there the boiler flow is set to 75 degrees which is the max and for the return coil it is quite hot when the hot water is on. And to confirm one full turn is adequate?
 
You can allways open it fully, if you all ready have it 4 turns open then its almost fully open anyway. If the cylinder is taking hours to heat up then the coil may have scale if its years old.
 
Should be able to slacken the pipe at the top where its connected to the coil and pull it back a little to allow the air to escape.
 
Does the air stop after a few seconds or does it take longer??.
If you have a sealed system ensure boiler pressure at 1/1.5bar, if open vented ensure the (small) F&E tank is "full" of water.
 
I have a 150L HW cylinder with a standard 0.65M2 coil, I took some readings off it when heating a stone cold cylinder from 13C to 60C years ago and my calcs showed that the coil averaged ~ 5kw output from cold to hot, ~ 8kw when cylinder cold and ~ 2kw with a hot cylinder, boiler temp was/is 70C.
Based on that, to heat a 100L cylinder from say 10C to 55C should take ~ 1 hour. A 150L 1.5hrs, 200L, 2hrs etc. These would now be considered very very slow heat up times.
So knowing the volume of your HW cylinde you can get a rough idea from my numbers the heat up time required.
 

Reply to Cylinder return valve? in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi guys, just want to get some advise, basically new vaillant regular boiler has been fitted approx 5 yrs ago, i believe it was back boiler...
Replies
0
Views
146
Hi all. This ‘valve’ is at the bottom of our domestic hot water cylinder. Anyone have any idea what it is please? It must’ve been there for many...
Replies
4
Views
419
Hello friends - I really struggle to understand my heating and hot water system I posted my question on Diynot but it ended up being five pages...
Replies
10
Views
782
Do most composite valves now for unvented cylinders have a tee on them For the expansion valve connection? The ones I used to fit just had the...
Replies
2
Views
279
Hi There was no shut off valve on the tank feed to the hot water cylinder, and I needed to move a couple of hot water pipes, so I shut off the...
Replies
4
Views
261
Back
Top