Hi
I have a valiant plus ecotec 418, ( about 8-9 years old ) it has always had the same problem, continually going from S.5.3 to S5.4 and back again....when ever I check, the Delta T while running normally is around 20oC and I am told S.5.3 doesn’t occur until the DT is 30oC. The boiler fires up very quick, but as the inlet temperature increases only slowly, I assume this is when the 30oC is reached.

it stays in the S.5.3 stage for around 10 minutes, goes to S5.4, then fires up, exceeds the DT then goes back to S.5.3..this cycle continues until eventually it settles down and stays at S.5.4......although even before that is achieved, it often fails to reduce firing, even when only 2oC away from the target temperature of 78oC and shuts down on over temperature.

Vaillant tell me it’s likely restricted or undersized pipe work, which could have been due to my ‘ not so very clever’ builder during my house extension in 2003. So if the boiler flow is less than it should be, that could explain why the boiler manages to achieve the outlet temperature so quickly ( I also reduced the KW to between 5-10KW from 18KW ) also if the flow is low, could that explain why the inlet temperature lags behind the outlet temperature so much ???

So would a higher capacity / flow CH pump be the solution ??? The igniter system on this boiler must be excellent, as it fires up so so many times every day, far more than I would consider normal.

thanks
 
Can you post some pictures

Is it a big system?
How many radiators?
Unvented hot water cylinder?
What size pipework?
 
10 radiators, vented cylinder, boiler is vailiant plus ecotec 418 (18KW )

not sure how to detail pipe sizes, assume they are standard, NOT microbore.....

hope images help 🤞
 

Attachments

  • 90F41A95-06F9-4822-B8C5-794CD1E74B35.jpeg
    90F41A95-06F9-4822-B8C5-794CD1E74B35.jpeg
    518.9 KB · Views: 35
  • DA5DE531-2D75-4913-9239-0AB5741D003B.jpeg
    DA5DE531-2D75-4913-9239-0AB5741D003B.jpeg
    405.9 KB · Views: 25
  • B66E5CB0-2D46-45F4-8FE1-C10C3E005F90.jpeg
    B66E5CB0-2D46-45F4-8FE1-C10C3E005F90.jpeg
    377.2 KB · Views: 26
  • 4A4075BB-0248-43A3-B8E8-350F4DF14689.jpeg
    4A4075BB-0248-43A3-B8E8-350F4DF14689.jpeg
    414.5 KB · Views: 33
Thanks. Boiler primaries appear to be 22mm which is fine for that boiler output and flow required. The pump seems to be discontinued now, so I am struggling to find a data sheet with pump curves etc.
It does initially sound like a flow problem (lack of). Any idea what the quality of system water is like? Are you aware of any sludge buildup or other corrosion? Id imagine with a perfectly healthy system and pump that pump would be fine but again I cant find any info, so might be wrong.
 
Thanks. Boiler primaries appear to be 22mm which is fine for that boiler output and flow required. The pump seems to be discontinued now, so I am struggling to find a data sheet with pump curves etc.
It does initially sound like a flow problem (lack of). Any idea what the quality of system water is like? Are you aware of any sludge buildup or other corrosion? Id imagine with a perfectly healthy system and pump that pump would be fine but again I cant find any info, so might be wrong.
Heating system in good condition, recently drained down, flushed with cleaner and then treated....the water was pretty much clear, save a little discolouration from one or two rads....used to flush every year....& re treat, then was advised, unless leaks or excessive air, then every 5 years or so is ok

emailed WILO and received the data sheet within 10 minutes, how’s that for customer service 👍
 

Attachments

  • C6843530-9E6F-4F73-B556-DE978518A586.png
    C6843530-9E6F-4F73-B556-DE978518A586.png
    464.4 KB · Views: 31
15-60 will be fine

but suspect the issue is your microbore pipe work
 
New posts

Reply to Central heating pump sizing in the USA area at PlumbersForums.net

Similar plumbing topics

My central heating is run off a heat pump ( air to water ) quite expensive to run , So I’m plainning to fit a wood burning with a back boiler to...
Replies
3
Views
298
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
284
MartinPod81
M
  • Sticky
I thought I'd create a master thread to move all of these similar threads into, over time like. If your central heating doesn't work boiler...
Replies
8
Views
1K
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
410
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
447

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock