Discuss Care home UFH wired incorrectly in the Underfloor Heating Forum area at UKPlumbersForums.co.uk.

  1. Michael Groves

    Michael Groves Member

    I’m an electrician, a plumber has asked me to look at wiring in a care home for UFH with a system boiler.
    Only way to get it to work is run everything constantly.
    The wiring center was a mess, i’ve rewired and now working as expected.
    However, it appears to me there is an unnecessary valve. On the heating side there is a master valve (S-Plan), then behind this two manifolds with thier own valves. The master valve was wired to be constantly open.
    I’ve rewired for it to only open when one of the UFH valves is calling for hot water.
    I’ve been told UFH was installed by one company and boiler by another. So I wonder if boiler engineer installed S-Plan, and UFH just fitted to this.
    I can’t see any reason for the master valve (S-Plan). I’m gonna suggest to plumber to remove as I just can’t see any reason for it and I think this will simplify installation, what do you think, am I missing something.
    To be clear I’m ignoring hot water in this post, that all works fine.
     
  2. Last Plumber

    Last Plumber Trusted Plumber GSR

    Photographs might help if you have any?
     
  3. Michael Groves

    Michael Groves Member

    Unfortunately I’m not back for a while, but photos probably won’t help anyway as the installation is spread out across the property.
    To put it another way, the installation has two valves in series. Is that normal with UFH?
     
  4. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    Zone valves wired in series ?
     
  5. Harvest Fields

    Harvest Fields S. Mod Trusted Plumber GSR Top Contributor!!

    Thought you previous said you was a landlord and not a sparks.
     
  6. Michael Groves

    Michael Groves Member

    I’m both.
     
  7. Michael Groves

    Michael Groves Member

    Plumbed in series. imagine;
    boiler
    valve
    pair of valves each with UFH manifold.

    I’ll try and post a diagram later if that does not make sense.
     
  8. Michael Groves

    Michael Groves Member

    Here's a brief diagram, hopefully this makes more sense than my text.
    To recap, I don't see why you need a "Master Valve"

    20190226_074439061_iOS.jpg
     
  9. Harvest Fields

    Harvest Fields S. Mod Trusted Plumber GSR Top Contributor!!

    Are there rads as well as UFH?
     
  10. Michael Groves

    Michael Groves Member

    No
     
  11. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    You sure it’s not a 3 port would make sense
     
  12. Michael Groves

    Michael Groves Member

    When you say "3 port" I guess you are referring to Harvest Fields suggestion as opposed to a 3 port valve?

    It would then make sense if this was the case. I will double check when I am back, but I was lead to believe there is only UFH.
    If this is the case, do you agree the "Master Valve" is superfluous ?
     
  13. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    No it could be a 3 port zone valve or are you 100% it’s a 2 port
     
  14. Harvest Fields

    Harvest Fields S. Mod Trusted Plumber GSR Top Contributor!!

    I am confused by what you mean by a master valve? Are there just 2 zone valves. If so you have to have these otherwise the under floor would only come on with the water and they will want the underfloor on by itself .
     
  15. Michael Groves

    Michael Groves Member

    Definitely a 2 port valve, 100% sure
     