I’m an electrician, a plumber has asked me to look at wiring in a care home for UFH with a system boiler.
Only way to get it to work is run everything constantly.
The wiring center was a mess, i’ve rewired and now working as expected.
However, it appears to me there is an unnecessary valve. On the heating side there is a master valve (S-Plan), then behind this two manifolds with thier own valves. The master valve was wired to be constantly open.
I’ve rewired for it to only open when one of the UFH valves is calling for hot water.
I’ve been told UFH was installed by one company and boiler by another. So I wonder if boiler engineer installed S-Plan, and UFH just fitted to this.
I can’t see any reason for the master valve (S-Plan). I’m gonna suggest to plumber to remove as I just can’t see any reason for it and I think this will simplify installation, what do you think, am I missing something.
To be clear I’m ignoring hot water in this post, that all works fine.
 
Zone valves wired in series ?
 
Here's a brief diagram, hopefully this makes more sense than my text.
To recap, I don't see why you need a "Master Valve"

20190226_074439061_iOS.jpg
 
You sure it’s not a 3 port would make sense
 
When you say "3 port" I guess you are referring to Harvest Fields suggestion as opposed to a 3 port valve?

It would then make sense if this was the case. I will double check when I am back, but I was lead to believe there is only UFH.
If this is the case, do you agree the "Master Valve" is superfluous ?

No it could be a 3 port zone valve or are you 100% it’s a 2 port
 
I am confused by what you mean by a master valve? Are there just 2 zone valves. If so you have to have these otherwise the under floor would only come on with the water and they will want the underfloor on by itself .
 
I am confused by what you mean by a master valve? Are there just 2 zone valves. If so you have to have these otherwise the under floor would only come on with the water and they will want the underfloor on by itself .
Master valve is my terminology as it governs the subordinate vavles, look at the diagram, it's in series with the manifold valves. The manifold valve triggers the boiler when any of the thermostats call for heat. All the thermostats are wired into a relay for this purpose.
 
Remove it then
 

Reply to Care home UFH wired incorrectly in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
114
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
0
Views
49
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
6
Views
133
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
219
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
346
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock