I've just had an air to water heat pump installed at my house, and I wanted to get a rough idea of what it's performance is. Can anyone help with a reasonably simple way to calculate the real world COP as a cross-check against the manufacturers BS?

I appreciate that COP is a crude measure, that it's only a snapshot, and that the average across the whole season is more useful etc etc, but indulge me for the sake of my curiosity.

The heat pump control tells me the inlet and outlet water temperatures, the Wilo circulation pump shows the water flow rate, and I have the electricity consumption metered separately. What would the formula be, and do I need any other measurements? Anyone?
 
The heat pump control tells me the inlet and outlet water temperatures, the Wilo circulation pump shows the water flow rate, and I have the electricity consumption metered separately. What would the formula be, and do I need any other measurements? Anyone?
The heat output is calculated using the formula: kW = flow x ΔT x 4.18

Flow is measured in litres/sec
ΔT is the difference between inlet and outlet temperature.

e.g

flow =0.5 l/sec
ΔT = 10°C

kW = 0.5 x 10 x 4.18 = 20.9kW

If the system produces this for one hour then 20.9 kWh will have been produced.

As well as knowing the electricity consumption you also need the time over which it was consumed. Only the time when the system is running is relevant.
 
doitmyself: Thanks for taking the time to help. So, the 4.18 is the specific heat of water I think? More importantly, can you expand a bit on your last point? How does the time get plugged into the equation? Come to that, exactly what is the equation? And am I right in thinking that COP is a snapshot taken at a point in time?
 
Which Wilo pump is it? Are you sure it's displaying flow and not power consumption or metres head?

Also, which heat pumps have you had installed?
 
It's the Stratos Pico circulation pump, and yes, it definitely shows flow rate. I'd like to keep to myself the heat pump make for the time being as I don't want the debate to get sidetracked by pros and cons of different brands. I don't think it's relevant to my original question is it?
 
Might be easier to get a heat meter installed along with an electricity meter to calculate seasonal COP that would be more useful for you.
 
Might be easier to get a heat meter installed along with an electricity meter to calculate seasonal COP that would be more useful for you.

Cheers. Yeah, I may do that eventually, but at the moment I just want a quick fix as a starting point.
 
So, the 4.18 is the specific heat of water I think? More importantly, can you expand a bit on your last point? How does the time get plugged into the equation? Come to that, exactly what is the equation?
You are right about 4.18.

As for time, remember that one watt is actually one Joule per second. So one kWh is therefore 3.6 Megajoules (1000 x 60 x 60).

If the system in my previous example runs for one minute it will produce 20.9 x 60 = 1254 Joules of energy. Let's say the electricity consumption over the minute is 0.1 kWh = 0.1 X 60 x 60 = 360 Joules. Then the COP is 1254/360 = 3.48.

I have no idea about the COP part of your question, but a snapshot seems the most likely method. It would be similar to the way a gas boiler is rated by measuring the gas consumption over two minutes. Measuring over a long time would be difficult as the temperatures would not be constant.
 
If the system in my previous example runs for one minute it will produce 20.9 x 60 = 1254 Joules of energy. Let's say the electricity consumption over the minute is 0.1 kWh = 0.1 X 60 x 60 = 360 Joules. Then the COP is 1254/360 = 3.48.
Sorry, but that's not correct. I forgot the kilo prefix. The heat produced is 1254 kJ and electricity used is 360 kJ. The COP doesn't change.
 
......As for time, remember that one watt is actually one Joule per second. So one kWh is therefore 3.6 Megajoules (1000 x 60 x 60).

If the system in my previous example runs for one minute it will produce 20.9 x 60 = 1254 Joules of energy. Let's say the electricity consumption over the minute is 0.1 kWh = 0.1 X 60 x 60 = 360 Joules. Then the COP is 1254/360 = 3.48.

OK, I'm struggling a bit with the maths.... My figures are as follows:

Flow rate: 66.66 litres per minute
DeltaT: 14 C
Energy produced = 66.66 x 14 x 4.18 = 3900 Joules
Electricity consumed: .067 kW per minute x 60 x 60 = 241 Joules
COP = 3900/241 = 16.2

A COP of 16.2 seems a little unlikely. Can you see what I am doing wrong? I'm sure it's really basic. I think all the 60s are confusing me. (Didn't see your second post, but as you say, it doesn't change the COP)
 
Joules confuse me, but 66.66 X 14 X 4 X 60 equals 224,000 BTU/hr Approx 67 Kw. This seems high. I would seek confirmation of flow rate or temp. diff.
 
Your DT is way to high which suggests a flow rate issue. The reason I asked about which heat pump you have is to understand its capabilities and whether or not it was an inverter driven compressor etc, not because I wanted to slag it of or suggest a different model.

When did you take the DT and under what conditions? You need to allow the heat pump to run for long enough for it to adjust to whatever load you're placing it under.
 
Joules confuse me, but 66.66 X 14 X 4 X 60 equals 224,000 BTU/hr Approx 67 Kw. This seems high. I would seek confirmation of flow rate or temp. diff.

Now I'm worried. The temp readings are on the heat pump control panel, reading off sensors inside. The numbers they give seem to make sense when compared with the operation of the thermostat on the buffer tank, and with the return temperature off the UFH as given by the manifold thermometers. Could be wrong, but they seem to stack up. The flow rate is off the Wilo circulation pump. This has an LCD screen that gives electricity consumption and flow rate amongst other things. I guess I'd assumed this would be reasonable reliable, given Wilo's reputation. Probably naive?
 
Your DT is way to high which suggests a flow rate issue. The reason I asked about which heat pump you have is to understand its capabilities and whether or not it was an inverter driven compressor etc, not because I wanted to slag it of or suggest a different model.

When did you take the DT and under what conditions? You need to allow the heat pump to run for long enough for it to adjust to whatever load you're placing it under.

It's not inverter driven. I wasn't thinking you were about to slag it off, but trust me that if I do mention the brand, there will be a whole chorus of jeering, telling me it's rubbish. I'm basing this on posts in other threads. Don't think it matters for now, I'll share later if people are interested.

The DT was even higher till I cranked up the flow rate!! The Wilo Stratos Pico has adjustable flow rate, and the screen readout tells me I'm at maximum at 4000 litres/hour.

I've been letting the heat pump run and stabilise, although to be honest, it makes little difference. Seems to start out at a DT of 14 and stay there with outlet temperature gradually rising from 43 to 48 when the thermostat cuts out. I mentioned in another post, that I'm running the heat pump into a buffer tank. Would that result in the stable DT? Why do you think it's high?
 
Last edited by a moderator:
Unfamiliar with pump, but does the 4000 litre/hr. refer to theoretical flow against zero head resistance.
 
Unfamiliar with pump, but does the 4000 litre/hr. refer to theoretical flow against zero head resistance.
Good question. No idea. Would have thought it was a bit odd to display theoretical flow rate on a changing display that can be adjusted by user? Dunno.
 
4000 seemed too round a figure for actual flow rate. Since posting I have goggled pump data and flow drops off considerably with head.
 
The heat pump does matter as the controller is what makes a lot of difference with a heat pump.

The basic principles aren't all that different for most heat pumps, maybe different refrigerant etc

How the heat pump output is controlled is another matter. I'm guessing it's a Dream or similar and this is a self fit / non RHI type install?

What size and type of pipework is used from the outdoor unit to the buffer and over what distance?

How is the buffer connected to the heat pump and system, is it in series/parallel, 2 pipe, 4 pipe etc etc

I'm afraid if you want help or answers you'll have to start disclosing more information.
 
OK, I'm struggling a bit with the maths.... My figures are as follows:

Flow rate: 66.66 litres per minute
If, as you say in a later post, the flow is 4m³/hr that is 66.66 litres/min. However, my formula needs the flow in litres/sec so the output is 66.66/60 x 14 x 4.18 = 65kW or 65 J/sec. The output over one minute is therefore 3900 Joules. (I know it's the same as you got but, as one of my maths teachers used to say, "right answer, wrong method!")

Your calculations are correct, but a COP of over 16 seems unlikely. You mentioned another post about a buffer tank, but I can't find it. A link would be useful.
 
4000 seemed too round a figure for actual flow rate. Since posting I have goggled pump data and flow drops off considerably with head.

OK, makes sense. I think there is a setting on the pump to tell it what head you are working with. Can't check now as weather is a bit dodgy. Will look tomorrow. I think it was set properly, but as you say, the 4000 sounds a bit nominal....

However, if I can get an accurate figure for flow, I still need confirmation that I am doing the sums right. Any help on that would be much appreciated.

For example, if I halve the flow rate, (seems extreme), I still get a COP of around 8, I think. Something still wrong?
 
It's not inverter driven. I wasn't thinking you were about to slag it off, but trust me that if I do mention the brand, there will be a whole chorus of jeering, telling me it's rubbish. I'm basing this on posts in other threads. Don't think it matters for now, I'll share later if people are interested.

The DT was even higher till I cranked up the flow rate!! The Wilo Stratos Pico has adjustable flow rate, and the screen readout tells me I'm at maximum at 4000 litres/hour.

I've been letting the heat pump run and stabilise, although to be honest, it makes little difference. Seems to start out at a DT of 14 and stay there with outlet temperature gradually rising from 43 to 48 when the thermostat cuts out. I mentioned in another post, that I'm running the heat pump into a buffer tank. Would that result in the stable DT? Why do you think it's high?

Do you have a pump valve you can throttle down to see if it effects the displayed flow rate on the display?

What size pump is it you've installed? Looking at the info, my guess would be a 1-6 which at max would give you a theoretical flow rate of about 4m3 p/hr, or 4000 litres...
 
Last edited:
Do you have a pump valve you can throttle down to see if it effects the displayed flow rate on the display?

What size pump is it you've installed?

Well, as already mentioned, there is an adjustment on the pump to reduce flow rate. When I knock that down, the pump goes quieter and the readout shows a lower electricity consumption, so I guess it's working. The pump is the Wilo Stratos Pico 30/1-4.

But as already touched on, if I reduce flow rate, the DT goes even higher.
 
The maths that arrive at 65Kw is agreed, from data based on flow and temp.
Of the two, temp. is easily verified, even by touch. Determination of flow will resolve the issue.
 
Well, as already mentioned, there is an adjustment on the pump to reduce flow rate. When I knock that down, the pump goes quieter and the readout shows a lower electricity consumption, so I guess it's working. The pump is the Wilo Stratos Pico 30/1-4.

But as already touched on, if I reduce flow rate, the DT goes even higher.

If the flow rate was measured then external influences (such as reducing flow through a valve) would effect the displayed flow rate. Adjusting the pump on its setting won't.

According to the Wilo data, the pump you've got won't even perform at the given flow rate, so I'd take that with a pinch of salt.

I think it's also safe to say the heat pump isn't providing 65kw, or a COP of 16 for that matter.

Until you can give more info, you won't get the answers you need. I suspect you have flow issues. I'd also be very surprised if you can get anywhere near an accurate COP unless you calculate the real time flow rate, which again requires info from the manufacturer.

Good luck.
 
Somethings wrong:

66 lpm is one heck of flow rate

Flow rate: 66.66 litres per minute
DeltaT: 14 C

= 65kW that is one heck of a heat load for a heat pump - in a domestic single phase environment the DNO wouldn't let you connect it...

I would expect and old leaky house of 600m2 for that load... That's one heck of sized house, and the radiators will be filling the walls :)

Two things sound wrong

1) Flow rate
2) delta T

We install Wilo pumps all the time, and they usually display either watts being consumed or m head.

If the system has been installed to proper standards, then installing a heat meter and electricity meter should be a very simple process. (installing them correctly requires some specific knowledge )

We do that quite often when the client really wants to know what's what.
 
Guys, many thanks. I think it's clear that the flow rate I had thought I was getting is well above the actual flow rate. Thanks for homing in on that.

As an aside, I should say that the heat pump is giving hot water in excess of 50 degrees, and the house is nicely warm via the UFH. (Not running DHW off this system.) So, I'm not unhappy with the system overall, but I am just curious about the actual COP compared to manuufacturers figure. Which is why I didn't initially go into lots of detail about the system. I just thought I would get a quicker answer about the COP calculation that way.

Nostrum: Good guess, in part! Yes, it's a Dream, no it's not a self-install.

So, my next move may be to try to find a heat meter, as someone suggested, since it seems I wont be able to work out an accurate figure using the Wilo display.

I can't work out what is wrong with my interpretation of the Wilo display. I'll check again when it is running. In the meantime here is a picture of it, showing how it displays the flow rate: stratos pico.jpg

I fully accept my figure is wrong. From the pump curves I have seen, (it's a 1-4), I would expect about 1750 litres per hour, given that my head is 1.70 metres? Not quite the same as 4000 per hour......

As to DT being wrong, I'm not convinced. As I mentioned before, the inlet and outlet temperatures seem to be what I would expect.
 
I think it's clear that the flow rate I had thought I was getting is well above the I would expect about 1750 litres per hour, given that my head is 1.70 metres?
I assume you have set the head to 1.7 metres. How did you arrive at this?

Which operating mode have you chosen Δp-c or Δp-v?

Is Dynamic Adapt turned on?
 
You will find that as the ambient (source temperature) drops that the pressure ratio/lift of the refrigeration circuit increases due to energy input increase and the COP will reduce vice versa
 
Inlet and outlet temperature may be correct...

If you are running at 50° I hope your not putting that into the underfloor, you'll cook it.

Your underfloor should have a blending / mixing valve on it that mixes the return with the flow to reduce it's temp and also it means that the flow around the UFH circuits won't be measurable from the wilo pump.

In practice when done properly (assume no radiators, or if they are they are correctly sized) the installer should have removed the mixing valves on the ufh manifolds and reduced the flow temperature, the heatpump will work much more efficiently producing greater flow at lower temp than lower flow at highertemp.
 
Do you have a copy of the heat Pump output curve supplied by the manufacturers?

It looks as though they only do a 10kw model, I'm guessing this would be at A7-W35? If we can have the above, you should be able to calculate the flow rate.

The consequence of a low flow rate will depend on how the heat pump controls operate. Quite likely it will just continue running at a higher flow temperature and higher fridge circuit pressure,which will over time increase wear on the compressor and reduce efficiency overall.
 
Last edited:
I assume you have set the head to 1.7 metres. How did you arrive at this?

Which operating mode have you chosen Δp-c or Δp-v?

Is Dynamic Adapt turned on?

My figure of 1.7 m is the measured height differential between the pump and the highest point of the circuit, the inlet to the buffer tank. Did I need to look at something more subtle?

I have not actually set this into the Wilo settings because if I do, my DT shoots up even higher and I eventually get a "Flow Rate Error" on the heat pump. At the moment I have the head set to 4m, (the maximum), and this stops the flow rate error message and gives me a DT of 14C.

I have Dp-c, which is what they recommend for UFH?

No sign of Dynamic Adapt in the instructions or on the display!
 
Do you have a copy of the heat Pump output curve supplied by the manufacturers?

It looks as though they only do a 10kw model, I'm guessing this would be at A7-W35? If we can have the above, you should be able to calculate the flow rate.

The consequence of a low flow rate will depend on how the heat pump controls operate. Quite likely it will just continue running at a higher flow temperature and higher fridge circuit pressure,which will over time increase wear on the compressor and reduce efficiency overall.

Guys, thanks again to everyone who is taking an interest. Sorry if I'm not responding to every post, but there seems to be some sort of lag where I reply to one post, and then see there was another earlier one that needs a reply. Or perhaps I'm just being confused by all the various posts and questions.

I don't have a heat curve, I'm afraid. It is claimed to be a 15 kW model, I think at A7-W40.

How can I reduce the DT? I cannot increase flow rate any more unless I get the more powerful circulation pump. Ambient air temperature around the heat pump is about 12C at the moment.
 
My figure of 1.7 m is the measured height differential between the pump and the highest point of the circuit, the inlet to the buffer tank. Did I need to look at something more subtle?
It's much more subtle than that.

Head has nothing to do with measuring the distance between pump and highest point. (I have even read post from "pro's" who didn't know this.) The head of a system is the pressure loss round the circuit due to friction caused by the water flowing. The pump has to overcome this loss and provide the required flow rate. I suspect that your pump may not be able to do this.

Stating the head in metres (of water) is an antiquated way of doing it. The better way is to quote the pressure loss in Bar or kPa.

Wilo recommend ΔP-C for a UF system, so stick with it.

What is the design temperature differential of the UF system?

How was the pump size determined?
 
If we assume that the heat pump is delivering 15kw, which given the outdoor temperature is probably fairly close, and with a DT of 15. We get a flow rate of 0.31 ltrs/second or 1130 ltrs/hr.

From what little information I can find on this heat pump, the specified flow rate is 2.2m3/hr, yours is 1.13m3/hr.

You've already stated the pump is on maximum, so we have to assume the flow rate is due to frictional loss within the circuit.

How is the heat pump piped in relation to the buffer? A picture would be the best way of showing this.

Worryingly, the pipe connections specified on this unit appear to be 3/4".
 
Status
Not open for further replies.

Reply to Calculation of thermal output??? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock