Now, been away for a bit and just noticed this post.
I truly believe some people require re-training in the basics here. Or maybe it is I that require the training.
You carry out a standard TT all (ie. appliances connected, cooker hood up) and have a 2 mbar drop with no smell of gas. It is
extremely unlikely this will ever grow to an explosive concentration so this is permitted under the rules/regs. Note on paperwork, walk away.
You then decide (needlessly) to take it amongst yourself to isolate all appliances and re-test. Low and behold you still have the 2 mbar drop.
You are then in effect testing the carcase only, which you are permitted a drop of 0 (zero) mbar. You have now opened the can of worms! You MUST now trace and repair this leak. If that means demolishing the customers house, so be it.
To walk away from this
knowing you have a 2 mbar drop with appliances isolated is in effect you walking away from a gas leak on the carcase. ie. an immediately dangerous situation.
If someone would like to correct my training/knowledge on this, all advice welcome.