I'm changing a top entry immersion tomorrow.. To date I've only done side entry.

I'm thinking I just need to shut off the gate valve on the cold feed (if it's not seized), run the lowest hot tap to drain pipework and then crack open the immersion - catching the excess with a wetvac.

Or is it best to drain the cylinder a little also?
 
Wouldn't bother draining the tank any Jayde. Just use the wet vac. You could always bung the tank to avoid the risk of the gate valve seizing in the shut position or letting by.
 
Wouldn't bother draining the tank any Jayde. Just use the wet vac. You could always bung the tank to avoid the risk of the gate valve seizing in the shut position or letting by.

True indeed. Cheers Paul
 
Bung Cwsc every time been caught out too many times seized gates on a Friday afternoon
Good luck
 
Bung Cwsc every time been caught out too many times seized gates on a Friday afternoon
Good luck

I will take your advice and go straight for the bung!!
 
did the job today - had no choice but to use the gate valve as it was communal water services in a mansion block. Was fine though, closed and opened nicely - surprisingly!! Glad I had my wetvac though as the bugger was letting by - but all was well in the world ;) thanks for your help fellas
 
Wouldn't bother draining the tank any Jayde. Just use the wet vac. You could always bung the tank to avoid the risk of the gate valve seizing in the shut position or letting by.

what will happen when the bung gets loose :D
 
Status
Not open for further replies.

Reply to Top Entry Immersion in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Got all my stuff together to finally fit the recirculation pump to my hot water tank, but I can't budge the immersion element. I need this out because a) I'm fitting solar which will be used to heat the hot water and although the fitted element has not been used so far, it's been in maybe 20...
Replies
11
Views
1K
First of all , a bit late but, a Happy New Year to everybody on the forum. Surely 2022 cannot be as strange as 2021, or can it? Anyway I digress. My question relates to entry positions on a radiator. I know for one that Stelrad say do not have bottom entry and top exit. This is supposedly to...
Replies
4
Views
925
Hello, my HW is taking longer than expected to heat up and it's getting worse. I can go 10-40 degs after 1.5 hours of only heating HW, whereas I should be going 10-60 degs in 30-40 mins by my maths. Don't even mention trying to heat HW and CH at the same time. 30 mins with the immersion adds...
Replies
2
Views
384
Hi, I'm new to the forum and just some background on myself. I have 4 years experience as a plumber but haven't worked in the trade in 15 years. I would say my overall knowledge is not great as I did most of the 4 years working on rinse and repeat estates of houses. I was also quite young and...
Replies
13
Views
582
Hello I want to replace the old single panel rad in the bedroom with a K2 double panel Stelrad one. I think I'm OK in general and relatively sensible (!) but I just want to check the steps involved to make sure I'm not missing anything before starting. System info- Steps (I think)- 1. Turn...
Replies
3
Views
919
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock