how many of you have ever done the air pressure test to a full ch system ?

me - never
 
Last edited:
I always air test my work where ever possible. Makes filling the system stress free.
 
only time i have ever pressure tested pipework is on commercial new builds, in domestic its pretty much water tested to 2 bar, leave to stand for 20-30 mins then heat tested
 
I've had too many faulty fittings over the years. I'd much rather hear the hiss of air than the drip of water.
 
ive air tested lots of stuff bepending on situations try to air test anything that will be impossible to access later under screed behind casings etc also depends whats below 3mil flats can contain a lot of exspensive stuff and their owners are well versed in the insurance claim game the smallest drip will be right on top of their favorite rembrant
 
never on heating systems only on gas carcus before screed goes down.
 
Status
Not open for further replies.

Reply to pressure test full ch system y plan in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello. I've just replaced our old Potterton EP2 CH controller with a Drayton Wiser HubR (& peripherals). The old backing plate wasn't...
Replies
1
Views
283
  • Question
I have a question that I’m hoping those of you who are experienced central heating engineers may be abler to throw some light on. But first I need...
Replies
6
Views
509
Customer complained of hot water tank getting hot when no demand Y plan system couldn't see any issues so I watched it Timer set to CH only, HW...
Replies
13
Views
2K
Hi, I have just installed a Tado system with the Wireless Reciever and Two Smart Thermostats. Without getting into the weeds of Tado, I want to...
Replies
5
Views
885
When I turn on our CH there's a lot of noise from one specific part of the system - the pipes on the landing, and one radiator. It sounds like...
Replies
35
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock