Good evening,

I had a cp12 carried out today on a vaillant combi.
The working pressure at the valve was 12.5mb and the engineer said minimum was 13mb on this boiler. All other test were ok, but he Ar'd it and asked me to turn it off. Is this correct as other test were fine (combustion and gas rate) it has been passed for the last 3 years

Cheers
 
It’s very low!
Do you have other appliances?
Pressure from the road can also drop at peak demand times and effect operation
 
I’m assuming it’s a different person/company the the previous years?
Yes a different company this time.
If combustion and gas rate are fine is it Ar or just not to regs. So could engineer make a note of it on certificate.
Boiler manual does state in the commissioning section if below 13mb not to turn boiler on.
 
That sounds as if it was installed without having the internal gas pipe correctly sized. Get a Gas Safe Registered engineer out and the problem can be resolved once and for all.
 
Hi
he did the correct thing. It now needs sorting.
it needs investigating as it could be a problem with the gas meter side or incoming main. Undersized pipework in your house. Or a boiler gas blockage.
all can be checked and remedied by a decent gas safe engineer.
 
It’s wrong and needs putting right.
It wasn’t fitted to regulations.
If you disagree you can get another CP12 from someone else or contact gas safe for a free inspection. They will go through it with the finest tooth comb and you will probably have a bigger list of faults to rectify.
 
If it's a let property it's (rightly) the landlords duty to keep it safe. I'd be glad I found someone who does the cp12 properly.
 
Thank you for your input. I just found it strange how it had passed before without any issue. However I met the engineer today and he explained and showed me why.

25kw boiler with 6m of 15mm copper which then joined 9m of 22mm copper which connected to the meter.

Only 1.5m of 15mm was visible at the boiler and the engineer had made a small hole in the ceiling revealing even more if it.

He is now coming back to re-run the entire thing and re-connect the boiler.
Disruption for the tenants but safety is paramount.
 

Reply to Cp12 has revealed Ar issue? in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi Folks I'm wondering anyone here, has any indepth knowledge on the Worcester Heatslave Combi Boiler. This boiler is quite old (2006) but it has...
Replies
10
Views
1K
Had our gas Baxi Combi inspected and serviced today, as it has been every year. Gas safety cert issued and says all okay, but engineer gave what I...
Replies
4
Views
586
Hi All, I need your advise as I'm really concerned here. I only just had regular boiler replaced with combi (Vaillant ecoFIT Pure 25kw). I had few...
Replies
10
Views
2K
Good Afternoon all, I am hopeful someone may be able to offer some guidance on the following. In the home we have a gas boiler (serviced...
Replies
5
Views
532
Hi there, I am hoping someone can give me some advice. We have had two leaks at home in the last 2 weeks; luckily we were in for both events and...
Replies
6
Views
838
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock