g60rge

Gas Engineer
Messages
94
Looking to swap out an old potterton on Promax 30 kW wall hung boiler at a mates house

he wants a vaillant, I suggested we get a like for like 30kw if all is working fine but noticed all pipe work to the boiler is 28mm

vaillant connections are 22mm, would i go up a size to the 438 to counter act this or will reducing near the boiler be sufficient?

I was thinking the potterton having 28mm pipes and connections helped it cope with so many rads
its a 20 rad system
 
Upsize to 28mm as close to the boiler as possible
22mm will only carry 24kw IIRC
 
I've been told that with new boilers they modulate down and will keep shutting down as it will keep circulating the closest rads

He said fit a low loss header or even zone off upstairs

My mate who is a Vaillant engineer said stick with a 430 as its upto the job
 
Does the existing set up work? If so then a like for like boiler swap will be fine. Most boilers have 22mm connections now so just reduce down as close as possible to the boiler.
If the existing set up isn't working, then think about altering it.
 
Should really be working out whole house heat loss the putting in the correct size boiler. Or at the very least range rating to the correct output. If he is thinking of ever having an extension put in a larger boiler than needed and range rating it.
 
Should really be working out whole house heat loss the putting in the correct size boiler. Or at the very least range rating to the correct output. If he is thinking of ever having an extension put in a larger boiler than needed and range rating it.

Definitely the right approach. Doesn't take that long to work out heat loss (loads of online calculators if you don't want to do it manually), and it may make a big difference in his bills...
 
heat loss calculator doesn't take into account how many rads are currently in the house though, if there are 20 rads and the calculator tells me i need 20kw, there will be a few stone cold rads right?

unhappy customer...
 
heat loss calculator doesn't take into account how many rads are currently in the house though, if there are 20 rads and the calculator tells me i need 20kw, there will be a few stone cold rads right?

unhappy customer...

heat loss the rooms and theres your kw then add 5kw for you cylinder
 
Status
Not open for further replies.

Reply to Boiler size question in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

A (if) CH system has a very high head loss due to improperly sized pipework and long runs and possibly partially blocked pipes and requires a UPS2...
Replies
16
Views
1K
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Replies
1
Views
339
Hi All, I am in the process of renovating a property and have the floorboards up installing cabling etc, however it is the plumbing that I have...
Replies
2
Views
1K
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
[ASIDE: I did wonder if this was the best forum for this but figured as it was a boiler related issue that the gas engineers would be dealing...
Replies
5
Views
273
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock