g60rge
Looking to swap out an old potterton on Promax 30 kW wall hung boiler at a mates house
he wants a vaillant, I suggested we get a like for like 30kw if all is working fine but noticed all pipe work to the boiler is 28mm
vaillant connections are 22mm, would i go up a size to the 438 to counter act this or will reducing near the boiler be sufficient?
I was thinking the potterton having 28mm pipes and connections helped it cope with so many rads
its a 20 rad system
Upsize to 28mm as close to the boiler as possible
22mm will only carry 24kw IIRC
I've been told that with new boilers they modulate down and will keep shutting down as it will keep circulating the closest rads
He said fit a low loss header or even zone off upstairs
My mate who is a Vaillant engineer said stick with a 430 as its upto the job
Does the existing set up work? If so then a like for like boiler swap will be fine. Most boilers have 22mm connections now so just reduce down as close as possible to the boiler.
If the existing set up isn't working, then think about altering it.
Should really be working out whole house heat loss the putting in the correct size boiler. Or at the very least range rating to the correct output. If he is thinking of ever having an extension put in a larger boiler than needed and range rating it.
Definitely the right approach. Doesn't take that long to work out heat loss (loads of online calculators if you don't want to do it manually), and it may make a big difference in his bills...
heat loss calculator doesn't take into account how many rads are currently in the house though, if there are 20 rads and the calculator tells me i need 20kw, there will be a few stone cold rads right?
unhappy customer...
unhappy customer...
heat loss the rooms and theres your kw then add 5kw for you cylinder
Reply to Boiler size question in the Plumbing Jobs | The Job-board area at PlumbersForums.net
A (if) CH system has a very high head loss due to improperly sized pipework and long runs and possibly partially blocked pipes and requires a UPS2...
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Hi All, I am in the process of renovating a property and have the floorboards up installing cabling etc, however it is the plumbing that I have...
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...