g60rge

Gas Engineer
Messages
94
Looking to swap out an old potterton on Promax 30 kW wall hung boiler at a mates house

he wants a vaillant, I suggested we get a like for like 30kw if all is working fine but noticed all pipe work to the boiler is 28mm

vaillant connections are 22mm, would i go up a size to the 438 to counter act this or will reducing near the boiler be sufficient?

I was thinking the potterton having 28mm pipes and connections helped it cope with so many rads
its a 20 rad system
 
Upsize to 28mm as close to the boiler as possible
22mm will only carry 24kw IIRC
 
I've been told that with new boilers they modulate down and will keep shutting down as it will keep circulating the closest rads

He said fit a low loss header or even zone off upstairs

My mate who is a Vaillant engineer said stick with a 430 as its upto the job
 
Does the existing set up work? If so then a like for like boiler swap will be fine. Most boilers have 22mm connections now so just reduce down as close as possible to the boiler.
If the existing set up isn't working, then think about altering it.
 
Should really be working out whole house heat loss the putting in the correct size boiler. Or at the very least range rating to the correct output. If he is thinking of ever having an extension put in a larger boiler than needed and range rating it.
 
Should really be working out whole house heat loss the putting in the correct size boiler. Or at the very least range rating to the correct output. If he is thinking of ever having an extension put in a larger boiler than needed and range rating it.

Definitely the right approach. Doesn't take that long to work out heat loss (loads of online calculators if you don't want to do it manually), and it may make a big difference in his bills...
 
heat loss calculator doesn't take into account how many rads are currently in the house though, if there are 20 rads and the calculator tells me i need 20kw, there will be a few stone cold rads right?

unhappy customer...
 
heat loss calculator doesn't take into account how many rads are currently in the house though, if there are 20 rads and the calculator tells me i need 20kw, there will be a few stone cold rads right?

unhappy customer...

heat loss the rooms and theres your kw then add 5kw for you cylinder
 
Status
Not open for further replies.

Reply to Boiler size question in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
205
P
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
245
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock