Thought isolation should be via a plug or fused switched spur? Came across one today that had just an isolator, no fuse.
But is it compliant?Probably thats all they had on the van .
Check that there is not another one somewhere else in the propertyThought isolation should be via a plug or fused switched spur? Came across one today that had just an isolator, no fuse.
There wasn’t.Check that there is not another one somewhere else in the property
I would quote them to get it changed.There wasn’t.
Off the ring.was it on its own supply? or off the ring
if oof the ring needs fusing
Off the ring.
Thought so. Need the isolating switch changing to fused switched spur.defo need to be fused
Thought so. Need the isolating switch changing to fused switched spur.
Absolutelyand down to 3 amp