arran197

Gas Engineer
Messages
1,288
A mate of mine has been to have a look at the above boiler with fault code expires E9 displayed. Apparently means seized pump, overheat stat fault or so he tells me. He's put a Grundfos 15-60 on it, it still didn't work after he swapped over the pump electrics, which I have now had a look at. The box on the side of the original pump has a pcb in it, live neutral and earth connections, but then also has another connection with 3 other wires going to it. The stat has continuity through it and when you run the boiler it kettles up quickly with no circulation.

Now I assume I'm barking up the right tree here, the pump had 240v on the live and a resistance of 152 ohms. I think it looks like the pcb has failed on the pump, it also smells a bit strange.

Anyone know if this sounds correct and that only the original type pump is suitable? It's an expensive part, with part number 87161063540.

Thanks.
 
british gas combi fault finding book mention Worcester bosch pump certain models cant be changed for just a head think its the 350 they mention
 
A mate of mine has been to have a look at the above boiler with fault code expires E9 displayed. Apparently means seized pump, overheat stat fault or so he tells me. He's put a Grundfos 15-60 on it, it still didn't work after he swapped over the pump electrics, which I have now had a look at. The box on the side of the original pump has a pcb in it, live neutral and earth connections, but then also has another connection with 3 other wires going to it. The stat has continuity through it and when you run the boiler it kettles up quickly with no circulation.

Now I assume I'm barking up the right tree here, the pump had 240v on the live and a resistance of 152 ohms. I think it looks like the pcb has failed on the pump, it also smells a bit strange.

Anyone know if this sounds correct and that only the original type pump is suitable? It's an expensive part, with part number 87161063540.

Thanks.

The three other wires you are talking about on the pump will be for modulating
 
That's what I assumed they were for. My mate swapped over all the electrics to the other pump, but that still didn't run. I think it's actually the pcb on the pump that's gone, so will have to get the whole thing. I think the customer is going to order it for us and we'll fit it, he's got the part number.
 
Yeah the pumps on cdi's are modulating so couldn't like to fit a regular grundfos head lol!

The last pump on a cdi I changed the pump bit was like brand new but the capacitor in the big electronic box on the side had a big split in it!!
 
ent it cheaper to buy the pump kit on these instead of just the pump head?? always best to replace part for part on the newer boilers......could get away with on the older non modulating pumps.
 
ent it cheaper to buy the pump kit on these instead of just the pump head?? always best to replace part for part on the newer boilers......could get away with on the older non modulating pumps.

Yes the pump kit is cheaper than the pump head does not make any sense.
 
Status
Not open for further replies.

Reply to Worcester Greenstar 30 CDI fault code E9 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
163
Sonya K
S
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
292
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
334
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock