any ideas

Worcester 34cdi classic newer type

Spot on burn 9.8 and 66ppm
Gas rate 33kw
Elec been changed

Going back Tom to check gas pressure gov
 
Why it’s still faulting ea

I’m out of ideas
 
Have you tried cleaning ionisation sensor Shaun?
I would replace them

Replaced they were fecked thought I sorted it as found the cause ran for a good 10 mins in service not a blip
 
Check the condense trap mate. I had one doing this where the white small bore pipe inside was kinked and not working correctly.

Done already that was shitty don’t think it’s been serviced tbh well not a decent one drive by more like
 
Touch wood done

Bearning plate was half stuck eg one side

So did the old pencil trick and no fault upto now

So will get a new one and return when I have time

Ta lads
 
Are they awkward to get to?

TBH very easy hardest part is getting the gas pipe out the bottom of the fan undo off gas valve also

Then undo the wires fan etc

Then two 10mm hex bolts at the top of the fan connecting onto the top burner

Remove fan and there’s your bearning plate left in

Only goes in one way 3 prongs etc
 
Yep common fault on these. The pencil trick followed by adjusting the fan overrun and fan startup rate stops it from recurring.
It's condensation forming on them normally. Adjusting the fan speed and overrun dries it out after use.


Process is as follows to prevent those nuisance recalls for ya.



Hold the spanner button until display changes (10 seconds) and shows 1a.
Release button. Use the eco button to navigate to "5b".
Press the chimney sweep button once. It will. Now glow orange and display current setting for that parameter (fan overrun).

Change this parameter to "18" (180 second fan overrun) using the "eco" button.

Press and hold chimney sweep button until display shows "[ ]"

Now hold both the "eco" button and the briefcase symbol button simultaneously and hold until displays shows "8A".

Press the "eco" button to navigate to parameter "9d"

Press the chimney sweep button once.
Change the parameter fan (start fan speed) using the eco button until it reads 55.

Press and hold chimney sweep button until display shows "[ ]"

Now press the spanner button once to exit service levels.

Hopefully that's clear and helpful.
 

Reply to ....Worcester ea.... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
275
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was prosecuted after Hereford Trading Standards Team found that he was falsely claiming to be on the Gas Safe Register when he was not, putting members of the...
Replies
0
Views
215
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
180
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
523
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
257
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock