B

beesley121

Hi guys,

got or a worcester 240 RSF not giving hw or heating on demand. When demand is put to boiler, pilot light ignites, spark electrode continues to spark even though the pilot is lit but the man burner will not ignite.
Put gauge on gas valve and Gas valve not opening.

Gas valve has has been replaced as British gas said gas valve had failed so customer ordered part and another engineer fitted it to no avail. I'm thinking pcb but I believe these boilers have a separate sequence pcb. Anyone had the same issue with this boiler? How would I know which pcb has failed?

Thanks in advance
 
had one it was the board but check flame sensing probe and wires 1st
 
I'd check the electrode, leads and earth. Make sure the pilot burner is clean and the flame is the correct length. Worcester are usually quite good on these cause they're old and most of the faults have been experienced before.
 
Had the same thing with a board on this boiler but as above could be flame rectification issue
 
I had one earlier today which wouldn't light ever since it was serviced. The flame sensing lead had been damaged. If not that and the electrode itself isn't damaged, then I would go for the ignition board.
 
Status
Not open for further replies.

Reply to Worcester 240 rsf - pilot ignite but not main burner in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Morco feb 24ed3 has a f1 fault code. The burner reading is fine. The fault is intermittent, sometimes the boiler won't ignite on either hot water...
Replies
0
Views
514
D
I have a Vaillant Turbomax with an F29 fault. When there is a demand for hot water the gas ignites initially, and the water is heated. However the...
Replies
7
Views
726
Deleted member 120897
D
F
Hi, My 2014 Crown Boiler has a spark ignition system that is malfunctioning. When I turn the boiler power switch off and back on, the pilot light...
Replies
1
Views
740
Hi all. I hope you are well. Need some advice on this boiler and fault. E229. Went there and condensate was totally blocked so cleaned it and...
Replies
0
Views
372
Conditions: nearly 10 year old boiler WB2B, heating mode off, DHW on or also in standby, Boiler shows no fault LED on, no new fault logged, room...
Replies
0
Views
413
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock