Old Account

hello guys,

I am wondering if anyone of you could tell if that makes any difference if you connect the flow and the return of the boiler the other way around on a uniSTORE unvented indirect cylinder?

Just came across an installation which some builders have done. Customer is complaining that the recharge is well over 1,5h for the hot water cylinder and therefore the boiler runs well too long - gas bill well too high.

Weirdly the builder has installed the flow with the zone valve for hot water at the bottom rather than at the top. Also the mains cold water pipe is very hot due to the fact that the pipe is right next to the flow.

I also noticed they did not install the vr10 sensor from the cylinder to the boiler which means the boiler will run almost continuously due to the controller setting on hot water constant.

Will that be one of the issues too?

The ufh is a joke too but see for yourself.
Any advise and tips are greatly appreciated.

Kind regards

Ron
 
Also too he is saying sometimes when heating is off and hot water is on constant he gets warm radiators. I have been there and checked if the zone valves working properly. They seem to open and close without problems but could that be that it’s letting by?

72162F23-BC3E-4C56-807E-0F948183D964.jpeg


F2F8849D-6AD3-4BC5-91CC-604F0A086B1B.jpeg
 
Also f &r should be the right way round. I’d doubt that it would make 1.5 hours difference but if the flow goes in the return the water will cool as it works up the coil
 
Where's the boiler in relation to the cylinder? The return does appear to be piped wrong allowing for backfeeding into the radiators as Riley has said. Also I can't see the wrong piping of flow and return into the cylinder making that much differnece, but I haven't came accross it before. Simple enough to repipe though and see if it makes a difference.

Fix the prv while your at it too o_O
 
Where's the boiler in relation to the cylinder? The return does appear to be piped wrong allowing for backfeeding into the radiators as Riley has said. Also I can't see the wrong piping of flow and return into the cylinder making that much differnece, but I haven't came accross it before. Simple enough to repipe though and see if it makes a difference.

Fix the prv while your at it too o_O
The boiler is in the kitchen which is about 5m away from the hallway where the cylinder is ( under the stairs.)!
 
If the hw isn’t the last tee back into the return then it could be back feeding some rads
I’m sorry Riley, any chance of simplifying this for me? As the flow is coming from the bottom the first T is the HW then CH. Are you saying it should be the other way around?
 
I wouldn’t think the F&R round the wrong way would mean it takes hours to heat up.
Is the flow temp set low?

Any auto bypass?
D2 not 300 before the bend
Does it goes into a washing machine upstand?
 
I wouldn’t think the F&R round the wrong way would mean it takes hours to heat up.
Is the flow temp set low?

Any auto bypass?
D2 not 300 before the bend
Does it goes into a washing machine upstand?
Flow temperature is set to 65c
Yes it goes into wm stand / wrong I know as well as the D2.
 

Reply to Vaillant System Boiler Q’s ... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
179
PSxxxxxx
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
231
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock