Old Account

hello guys,

I am wondering if anyone of you could tell if that makes any difference if you connect the flow and the return of the boiler the other way around on a uniSTORE unvented indirect cylinder?

Just came across an installation which some builders have done. Customer is complaining that the recharge is well over 1,5h for the hot water cylinder and therefore the boiler runs well too long - gas bill well too high.

Weirdly the builder has installed the flow with the zone valve for hot water at the bottom rather than at the top. Also the mains cold water pipe is very hot due to the fact that the pipe is right next to the flow.

I also noticed they did not install the vr10 sensor from the cylinder to the boiler which means the boiler will run almost continuously due to the controller setting on hot water constant.

Will that be one of the issues too?

The ufh is a joke too but see for yourself.
Any advise and tips are greatly appreciated.

Kind regards

Ron
 
Also too he is saying sometimes when heating is off and hot water is on constant he gets warm radiators. I have been there and checked if the zone valves working properly. They seem to open and close without problems but could that be that it’s letting by?

72162F23-BC3E-4C56-807E-0F948183D964.jpeg


F2F8849D-6AD3-4BC5-91CC-604F0A086B1B.jpeg
 
Also f &r should be the right way round. I’d doubt that it would make 1.5 hours difference but if the flow goes in the return the water will cool as it works up the coil
 
Where's the boiler in relation to the cylinder? The return does appear to be piped wrong allowing for backfeeding into the radiators as Riley has said. Also I can't see the wrong piping of flow and return into the cylinder making that much differnece, but I haven't came accross it before. Simple enough to repipe though and see if it makes a difference.

Fix the prv while your at it too o_O
 
Where's the boiler in relation to the cylinder? The return does appear to be piped wrong allowing for backfeeding into the radiators as Riley has said. Also I can't see the wrong piping of flow and return into the cylinder making that much differnece, but I haven't came accross it before. Simple enough to repipe though and see if it makes a difference.

Fix the prv while your at it too o_O
The boiler is in the kitchen which is about 5m away from the hallway where the cylinder is ( under the stairs.)!
 
If the hw isn’t the last tee back into the return then it could be back feeding some rads
I’m sorry Riley, any chance of simplifying this for me? As the flow is coming from the bottom the first T is the HW then CH. Are you saying it should be the other way around?
 
I wouldn’t think the F&R round the wrong way would mean it takes hours to heat up.
Is the flow temp set low?

Any auto bypass?
D2 not 300 before the bend
Does it goes into a washing machine upstand?
 
I wouldn’t think the F&R round the wrong way would mean it takes hours to heat up.
Is the flow temp set low?

Any auto bypass?
D2 not 300 before the bend
Does it goes into a washing machine upstand?
Flow temperature is set to 65c
Yes it goes into wm stand / wrong I know as well as the D2.
 

Reply to Vaillant System Boiler Q’s ... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I was hoping to replace an old system boiler with a Vaillant Ecotec Exclusive 627 system boiler, thats the one with the diverter valve so no need for zone valves, controling it with a V-Smart and a VR10. I've spoken to Vaillant Tech and they said you cannot use the VR10 with a vented...
Replies
0
Views
119
Hi, i've got a job with a Vaillant Ecotec 630 system boiler, and i don't know the full history but the house has definitely been extended significantly since the boiler was installed. There's now 21 radiators/towel rails. It's getting to temperature, but even after balancing, it's not heating...
Replies
2
Views
557
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig cupboard & a megaflo (no tank in loft). However the exisiting boiler is Vaillant ecoTEC 4xx boiler - which is satated by vaillant as an "open vent" boiler...
Replies
3
Views
454
Hello friends - I really struggle to understand my heating and hot water system I posted my question on Diynot but it ended up being five pages and couldnt get to the bottom of it and I thought worth asking the elders on here for their view - Hot water temp is 40 Degrees - Ideal Mexico 2...
Replies
10
Views
707
I just had a quote for a new boiler install as follows I dont undertand why a 15-60 boiler pump is needed and a 25-100 pump is needed as well I currently have an ideal mexico 2 heat only boiler - It has one DAB pump on the boiler return and a 2 port valve at the flow pipe to allow for heating...
Replies
3
Views
540
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock