This boiler even with a big call for CH Iwhere the bypass would/should be shut in any case if installed only occasionally gets up to 60C so maybe some other problem. One of the main reasons for a external bypass is to dissipate some heat with boiler shutdown and pump overrun, another is to keep the flow/return < Say 30C with very low circulation flows. Some boilers, probably with SS HXs don't require them. ABVs don,t work with modulating circ pumps IN PP mode and need very careful adjustment with pump in CP mode hence the recommendation above for a manual bypass.
 
Internal bypass is fine, you won't need an external one. That's what it's there for.

I'd set your pump to 100% on d.014 and it maybe that you bypass wants adjusting internally on the boiler, which your plumber will need to do.

And put Partial load back to Auto.
Thanks a lot! Looks like this solved the issue - added 1 full turn on the internal bypass, set output to Auto and now it goes to 60 degrees flow straight away! And now it's wired in a way that radiators zone valves open when UFH is ON to make sure that there is some flow through towel rads (we have 3 of them). So I believe it will be ok without additional bypass
 
Thanks a lot! Looks like this solved the issue - added 1 full turn on the internal bypass, set output to Auto and now it goes to 60 degrees flow straight away! And now it's wired in a way that radiators zone valves open when UFH is ON to make sure that there is some flow through towel rads (we have 3 of them). So I believe it will be ok without additional bypass
No problem 😎
 
Thanks a lot! Looks like this solved the issue - added 1 full turn on the internal bypass, set output to Auto and now it goes to 60 degrees flow straight away! And now it's wired in a way that radiators zone valves open when UFH is ON to make sure that there is some flow through towel rads (we have 3 of them). So I believe it will be ok without additional bypass

That's great to hear, you suspected the flow rate originally,
It would be interesting to see if you now can on UFH only or rads only

Did you also increase the pump speed to 100%?,
Also if you get a chance you might post the flow and return temps.

Thanks.
 
That's great to hear, you suspected the flow rate originally,
It would be interesting to see if you now can on UFH only or rads only

Did you also increase the pump speed to 100%?,
Also if you get a chance you might post the flow and return temps.

Thanks.

Can't log in on this PC for some reason or other.
 
Please define reset ? You have to change it every time you try and log on ?
 
If I log off or just exit the forum without logging off and go back in it asks me to log on, it then displays my user name and saved(correct) password but when i select log in nothing happens so I then select "forgot password" it then directs me to my given email and asks me for new password + confirmation, I then enter my (saved )+confirmed) password and press save and I am then logged in, the same happens in the central heating forum but not in the Electrical forum (different user name).
 
Last edited:
That's great to hear, you suspected the flow rate originally,
It would be interesting to see if you now can on UFH only or rads only

Did you also increase the pump speed to 100%?,
Also if you get a chance you might post the flow and return temps.

Thanks.
Pump was always at 100%. Will post some charts on temps later
 

Reply to Vaillant EcoTec Plus 938 temperamental in heating mode in the USA area at PlumbersForums.net

Similar plumbing topics

I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
808
Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd...
Replies
1
Views
424
Hello everyone, I'm facing an issue with my Vaillant EcoTec 832 boiler and would greatly appreciate your expert advice. The Problem: Heating...
Replies
8
Views
979
Hi I'm dealing with Vaillant Ecotec 824 R1 in one flat. The boiler make a very loud noise when central heating is on - this is random and occurs...
Replies
0
Views
437
Hi everyone, I'm hoping to get some advice on an issue I'm having with my Vaillant Ecotec Pro 24 boiler (R1 PCB). It was installed in 2013 and has...
Replies
1
Views
214
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock