This boiler even with a big call for CH Iwhere the bypass would/should be shut in any case if installed only occasionally gets up to 60C so maybe some other problem. One of the main reasons for a external bypass is to dissipate some heat with boiler shutdown and pump overrun, another is to keep the flow/return < Say 30C with very low circulation flows. Some boilers, probably with SS HXs don't require them. ABVs don,t work with modulating circ pumps IN PP mode and need very careful adjustment with pump in CP mode hence the recommendation above for a manual bypass.