The 938 is a huge output boiler have you worked out your heating load ? It maybe that it needs to be down rated, Valliants don't like being restricted it's trying to produce heat and the hive trvs and ufh controls are holding it back ? is there an auto bypass fitted a good way from the boiler ? I would advise having one fitted before the ufh Zone valve ? you need a flow rate though the boiler for pump over run this can't be restricted a good way of doing this is with a low loss header, try down rating it to 20 kw on the heating , can you post a picture of your install ? . Kop
 
Well, there is no d.029. After d.028 it goes straight to d.033. Why?

Could it be that the diverter valve gets stuck in DHW mode?

There is no mention of d.029 in the 418 manual so more than likely not available in your model.

Did you check d.017?
Check Target flow temperature d.005 and note d.071 setting.
Also check flow and return temperatures, d.040 & d.041

Also ensure that the boiler is actually running at low power and not firing up and then burner cut out with pump overrun and anti cycle time, the anti cycle time is shown in d.002 and factory setting is 20 minutes but the actual anticycle time is also dependent on the target temperature so if the target flow temp is 60C then the anticycle time is 6 minutes, you can read it (setting) off the table.

As KOP pointed out you can also de rate the boiler output (range rating) (in CH mode) so see what you come up with, with above readings first., just take d.000 off auto and insert your own rating maybe 10kw to start with??. it will not affect the DHW performance of 38kw.
 
Last edited:
D.017 is set to 0: Flow control. Target flow is set to 61. I changed partial load from Auto to 9KW for now and will monitor it.

There is no external bypass valve installed. I thought there is an internal one. Is it not good enough?
 
The internal one isn’t rated for external loads it’s only for the boiler when it’s doing it’s thing
 
You can set a towel rad to full open as long as it gives bypass when any zone valves close.

You can also calculate the flow rate, set the output to say 7 kw (as low as you can without burner cut out) with steady conditions then read off d.040&d.041. your flowrate LPM = 7*860/60/(d.040-d.041).
 
Last edited:
OK, looks like need to talk to our plumber (if I can find him - it was installed 2 years ago)
Internal bypass is fine, you won't need an external one. That's what it's there for.

I'd set your pump to 100% on d.014 and it maybe that you bypass wants adjusting internally on the boiler, which your plumber will need to do.

And put Partial load back to Auto.
 
Mr Evil is correct in his assumption the manufactures instructions states another auto bypass is not needed and the internal one is adjustable.
But although the boiler can handle the flow rate the system in my opinion needs One, there could be a lot of restriction on that system when rads or the ufh circuits begin to shut down it just makes it quieter and less harsh on the boiler and it's internal components, I've experienced this to a point where you have the same temperature going out as you have coming back the boiler gets confused starts cycling on and off that's no good for efficiency the boiler needs setting to its required kw output, flow rate, and cycling times in the installer menu this really isn't a DIY job has the temperature across the system flow and return been measured and recorded in the benchmark? every job requires commissioning and time spent fine tuning this is just my experience and some on here will agree others may not we're all have our ways of working . Regards Kop
 

Reply to Vaillant EcoTec Plus 938 temperamental in heating mode in the USA area at PlumbersForums.net

Similar plumbing topics

I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
810
Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd...
Replies
1
Views
424
Hello everyone, I'm facing an issue with my Vaillant EcoTec 832 boiler and would greatly appreciate your expert advice. The Problem: Heating...
Replies
8
Views
980
Hi I'm dealing with Vaillant Ecotec 824 R1 in one flat. The boiler make a very loud noise when central heating is on - this is random and occurs...
Replies
0
Views
438
Hi everyone, I'm hoping to get some advice on an issue I'm having with my Vaillant Ecotec Pro 24 boiler (R1 PCB). It was installed in 2013 and has...
Replies
1
Views
214
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock