Thanks. I'm not sure what the 24v link is I'm afraid. There is a wee junction box floating around underneath the boiler. Is that it?

I was not standing next to them while they were working but I did notice at some stage they had opened up the pump in order to remove air. That led to some water spillage.

Just now I switched on the hot water at the timer. This appeared to make the boiler more reluctant to fire which I did not expect. The boiler now seemed to be shedding heat through the pipe to the hot water tank but with the boiler off.

CH man said he would replace the automatic air valve on top of the boiler tomorrow, and generally do some diagnostic pondering. I can see his point in that, as they did not do anything other than replace radiatiors, and then struggle with air, some trapped air may be gumming up the works. Why that would make the boiler get stuck in this S7 - S8 - S7 loop, and keep the water hot in the bypass loop I even though heat is not asked for I find mysterious.
S.07 is the pump overrun time, default setting (D.01) 5 mins. S.08 is Temporary shutdown after heating procedure. Not sure if this is the anti cycle time (D.02), default setting 20 mins but the actual anti cycle time then depends on the heating target temperature, if the target temperature is 70C then the anti cycling time is 2.5 minutes with the 20 min default setting.
Reasons for above?: normal behaviour after heating or DHW period. If the boiler reaches its target temperature +5C for whatever reason, boiler minimum output > heating demand, or, perhaps in this case, mot.valves shut but boiler firing due to faulty end switch, or maybe this 24V link left in.
Apart from the above problem I hope the engineers havn't changed the pump settings causing this pump over into the (feed and expansion) tank as these systems can be very sensitive to the pump settings.

Hopefully, tomorrow will bring some answers.
 
S.07 is the pump overrun time, default setting (D.01) 5 mins. S.08 is Temporary shutdown after heating procedure. Not sure if this is the anti cycle time (D.02), default setting 20 mins but the actual anti cycle time then depends on the heating target temperature, if the target temperature is 70C then the anti cycling time is 2.5 minutes with the 20 min default setting.
Reasons for above?: normal behaviour after heating or DHW period. If the boiler reaches its target temperature +5C for whatever reason, boiler minimum output > heating demand, or, perhaps in this case, mot.valves shut but boiler firing due to faulty end switch, or maybe this 24V link left in.
Apart from the above problem I hope the engineers havn't changed the pump settings causing this pump over into the (feed and expansion) tank as these systems can be very sensitive to the pump settings.

Hopefully, tomorrow will bring some answers.
Thanks. The problem has evolved in that now, when I switch the hot water off at the timer, the boiler accepts this after a while and produces an S30 status. The pump then switches off. As far as I can see, that is what it should do.

As long as the hot water is not switched off, the pump will keep on running regardless of whether the boiler fires or not. The boiler will occasionally fire up in very short bursts lasting maybe 10 or 20 seconds. In my ignorance of the ways of boilers, I would have thought that firing until the hot water tank had reached the temperature set by its thermostat, and then calling it a day until the tank thermostat calls for heat would be logical.

I'll ask the CH man to check if the tank thermostat actually closes the HW valve underneath the boiler.
 
Vaillant boilers fires up at a high firing rate of approx 65%, they remain at this rate for up to 60 secs and then modulate down to the required firing rate, if the target flow temperature reaches SP+5C then the boiler will start cycling, the circ pump will IMO continue to run, when the anti cycling time has elapsed the boiler will fire up again. It looks possibly like air still in the system, can you fire up the boiler with both CH & HW requested, if it does remain firing, after a few minutes shut off CH and see if it remains firing on HW only.

Also ensure that there is water in the Feed & expansion tank.
 
Last edited:
Thanks. The problem has evolved in that now, when I switch the hot water off at the timer, the boiler accepts this after a while and produces an S30 status. The pump then switches off. As far as I can see, that is what it should do.

As long as the hot water is not switched off, the pump will keep on running regardless of whether the boiler fires or not. The boiler will occasionally fire up in very short bursts lasting maybe 10 or 20 seconds. In my ignorance of the ways of boilers, I would have thought that firing until the hot water tank had reached the temperature set by its thermostat, and then calling it a day until the tank thermostat calls for heat would be logical.

I'll ask the CH man to check if the tank thermostat actually closes the HW valve underneath the boiler.

Did you manage to resolve what it was?
 

Reply to Vaillant Ecotec plus 428 overactive. Keeps running in S7 and S8 mode. in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi I'm dealing with Vaillant Ecotec 824 R1 in one flat. The boiler make a very loud noise when central heating is on - this is random and occurs...
Replies
0
Views
435
My son has just had a new boiler fitted and hes noticed that the pump runs 24x7 even when both the heating and hot water are set to off. He’s...
Replies
3
Views
386
Hi everyone, I'm hoping to get some advice on an issue I'm having with my Vaillant Ecotec Pro 24 boiler (R1 PCB). It was installed in 2013 and has...
Replies
1
Views
211
Hello, I am looking for a heating engineer to diagnose and resolve an issue with my Vaillant EcoTec 832 combi boiler. Job Location: Copeland Rd...
Replies
1
Views
424
I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
805
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock