Matt0029

Gas Engineer
Messages
1,137
On an unvented cylinder if the expansion vessel has lost its charge. Can this still be the cause of dripping/discharge from the temperature relief valve. Or if the expansion had lost its charge would it discharge through the pressure relief on the composite valve? Thanks
 
If the expansion vessel had lost its charge I'd expect the expansion relief valve to act first, unless itself was faulty. If the combined temperature and pressure relief is discharging that symbolises other problems. Either can be affected by a number of things. If you're not G3 then best get someone who is to attend.
 
I am g3 yes. I've had it before were the pressure relief on the composite valve has dripped as the expansion has vessel has lost it charge. The expansion has lost it charge its charge on this one. The temperature relief has its own tundish on it and is dripping I cant tell if the pressure relief is dripping too as its combined after the tundish.
 
Is there anyway you can catch the drip from combined temperature and pressure relief and check pipe termination for possible expansion relief drip? Having said that that is installed wrong and both need to terminate into D1 of tundish.
 
Is there anyway you can catch the drip from combined temperature and pressure relief and check pipe termination for possible expansion relief drip? Having said that that is installed wrong and both need to terminate into D1 of tundish.
Yes I release it is installed wrong. I will recharge the expansion vessel before I go any further.
 
If the vessel had lost its charge, too much charge or failed altogether, or the pressure reducing valve had failed or not present then the expansion relief valve SHOULD drip first as its pressure setting is usually 1 bar lower than the combined pressure and temperature relief valve. The only time I would expect the combined pressure and temperature relief valve to activate due to excess pressure is if there's a problem with one of the above and the expansion relief valve had failed.

Edit: If there was a problem with a mixer unit letting by then any cold mains pressure not balanced and at higher pressure than supply to cylinder can also cause this problem.
 
Last edited:
If one uses the balanced supply and there is a problem meaning the valve to the unvented needs to be shut off - the property loses all water. Is this a usual scenario?
 
If the vessel had lost its charge, too much charge or failed altogether, or the pressure reducing valve had failed or not present then the expansion relief valve SHOULD drip first as its pressure setting is usually 1 bar lower than the combined pressure and temperature relief valve. The only time I would expect the combined pressure and temperature relief valve to activate due to excess pressure is if there's a problem with one of the above and the expansion relief valve had failed.

Edit: If there was a problem with a mixer unit letting by then any cold mains pressure not balanced and at higher pressure than supply to cylinder can also cause this problem.
In my experience the T&P always drips when expansion has failed. Agreed in theory the PRV at 6/7 should activate first, however from what I have seen they don’t. You also have to remember the T&P only start dripping, not discharging. They can start dripping at 6/7 bar before their set point.
 
If one uses the balanced supply and there is a problem meaning the valve to the unvented needs to be shut off - the property loses all water. Is this a usual scenario?
The one I'm looking at just has the balanced cold caped on the composite valve. I'm not sure if there's another pressure reducing valve on the mains. So back pressure could be an issue too I guess.
 

Reply to Temperature relief valve dripping in the USA area at PlumbersForums.net

Similar plumbing topics

Morning All I have a Megaflo unvented cylinder . Water had been dripping into the tundish so I tried to recharge the air gap, but when I went to...
Replies
1
Views
423
Hi. I replaced the Pressure and Temperature relief valve on my MegaFlo CL300 (I had thought it was dripping but it turns out the overflow drip...
Replies
2
Views
485
I have a Bristan Manhattan mixer tap in the kitchen. Five years ago, it started to drip. I replaced the valve in the cold water side and the...
Replies
1
Views
420
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air...
Replies
8
Views
312
W
Hi all. So I have an OSO Super SXD 180 immersion heater and it is pouring a huge amount of water out of the cold water pressure relief valve...
Replies
2
Views
595
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock