I went to another ideal logic today. 8 years old with the same problem. Can I ask how long do you need to leave the boiler to cool do. I went and dryed the area out again under the hex and uped the pressure and it stated leaking down again. The hex was pretty warm though still for using the shower an hour or 2 ago. Do you usually get condensation tuning down from the hex when the boiler is operating?
 
shouldnt leak much after its stopped (condense) normally if its alot its split
 
If its the heat exchanger it should be fairly obvious by the colour of the trap water.
Did you get the job of replacing the boiler?
 
Yes Shaun I could see it dripping from the back of the hex too when I removed the little cover of the front of the fluing system. I guess there shouldn't be any water dripping from the hex even when hot? As the condensate all comes down the front through the inner flue duct and back to the trap.
[automerge]1590951540[/automerge]
If its the heat exchanger it should be fairly obvious by the colour of the trap water.
Did you get the job of replacing the boiler?
This is a different boiler. But looks to be same problem. Yes I did swap the Las one.
 

Reply to Split heat exchanger on ideal logic in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Has anyone else come across this situation? I keep detecting products of combustion inside the casing of Ideal Logic boilers. I've replaced every...
Replies
6
Views
334
Got fd code on Ideal Logic Heat 15. Had two plumbers out and no joy. It’s had a new water flow sensor, flush with sentinel x800 and refurbished...
Replies
16
Views
674
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Hi, Boiler is losing pressure, from 1.5 bar to 0 bar in about 4 hours. Have checked all rads and seem to be fine, no water out external prv...
Replies
5
Views
658
I have a thermal store heated by a boiler with its own thermostat. I also have a stove with a back boiler. The stove heats water in a separate...
Replies
2
Views
475
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock