Looks like, as I warned, pipe stat is on wrong pipe!
It should NOT be fitted onto the primary flow as that pipe will become extremely hot rapidly and maintain a high temperature.
It needs to be after the heat is lost to the cylinder - on the return at bottom of cylinder.
Needs also to be set to a temperature that switches pump on long before the solid fuel pipes boil.
Best you get a heating engineer that is experienced in solid fuel systems to check everything out.