Right guys been and converted a system to sealed from ov today but can't get any heat at the rads we located the new boiler in the cupboard where the cylinder was used the 28 mm flow and return from the cylinder to connect to the heating flow and return at the back boiler but no heat at rads one thing I found. Funny was the. Heating flow and return from the bbu go off in 22 for a foot and then go to 15 there's a rad in the lounge which goes off the 22 before it rduces which got boiling that was turned off but still nothing the flow at a few of the rads is Luke warm but that's it any suggestions please. Let me know
regards Ryan
 
Antigravity valve fitted somewhere ?
Yep this......take off boxing in on chimney breast, and you will find a spring loaded valve, drain and remove, above assumes you have piped the BBU through correctly and piped old pump through without cutting off upstairs return, this will be a tee behind where you removed the old pump.
 
I know what the valve is not its like a non return valve should have said the boiler we have put in is a combi what do you mean by the upstairs return there were four pipes 2x22 2x28 I would hav o assume the 22 are the heating f and r and the 28 the hw f&r
 
Nothing was capped just linked 28 to 22 it shouldn't matter what is f& r as it will run either way ? I feel so stupid with this I should be able to rectify it but I'm just stumped thanks
 
Nothing was capped just linked 28 to 22 it shouldn't matter what is f& r as it will run either way ? I feel so stupid with this I should be able to rectify it but I'm just stumped thanks
It does if the pump was down stairs, where was it fitted it would have to have been piped through
 
Is there a NRV? if so it does matter also which way it was piped as it will not run either way, guessed it was a combi as you removed cylinder lol to use circs
 
Last edited by a moderator:
The 15mm flow and return is confusing me why would someone do that
Flow will have split from 22mm to 15mm up and down on chimney breast, correct? It was probably solid fuel converted to gas at some point, so it was how it was done then as it would almost boil round, with the pump to assist
 
Bbu had 2 outlets both had ch flow / rtn and was teed off in 28 to cylinder I was a bit stumped when I saw that tbh as there aren't many bbu round here so not removed many
 
Pump on return with what looked like a nrv after it going into the boiler
Check for another NRV on old ch flow on chimney breast, only answer and think you have some how reversed original F & R, ask customer if upstairs rads used to come on with JUST hot water on on BBU, IF THEY DID NOT AN NRV IS FITTED
 
Unless there's on on the return for the other rads as the only rad working is the one teed off the 22
Can you post up a drawing off how it was piped? And is now.... it would also work on rad if you had crossed F&R as flow would use old upstairs return that would have been behind old pump!
 