Gary80gas

Gas Engineer
Messages
164
From cold boiler pressure shoots up in seconds and dumps through prv whether hot water or heating. If you persevere with heating and get it running even on very low heat all settles down and boiler works fine, heating and hot water. Let system go cold and run hot water and system dumps again. I don't understand why it all runs ok with as little as 20deg of heating or higher. Puzzling. Any advice appreciated.
 
Im not sure if its blocked or not. Once the heating is running even at the lowest possible temp for a few minutes it all operates ok. Let it go cold and call for heat and the pressure flies up and discharges.
 
I got invited back again and solved it. I took the plug out the pump front and this time the pump would spin and stop, spin and stop. I checked power was continuous and so changed PUMP. I can only guess that the pump was warming up before and this is why it always worked once it was running. Also I should mention our favourite friends with penguins, it was under contract, had said they were not touching it because it definitely needed a power flush and extra air vents above boiler cutting in, all for bargain price of nearly £1400. Needless to say the water was clean and all it needed was a pump head change. Second occasion this year Ive found them making a serious misdiagnosis and profitable work for themselves. Not good enough.
 

Reply to Pressure problem with alpha cb25 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
161
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
170
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
238
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
384
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
504
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock