D

Devonplumber

Evening gents I have been trying to work out pipe loads but have be unable to find any formula or charts to help. Can anyone tell me the kw carrying capabilities at 1.5ls with 20c drop on 35mm,42mm,54mm,2.5"'3",4"?
 
Evening gents I have been trying to work out pipe loads but have be unable to find any formula or charts to help. Can anyone tell me the kw carrying capabilities at 1.5ls with 20c drop on 35mm,42mm,54mm,2.5"'3",4"?

any reason why?

isn't this normally left to mechanical engineers design specs?
 
I have been fitting biomass for 3 years and want to move on to design but everyone you ask doesn't want to tell you wait they already know.
 
35mm - 62kw @ 20DT
42mm - 100kw
54mm - 160kw
67mm - 235kw
76mm - 310kw
108mm - 650kw
past that and your into mechanical engineer realms,
 
Doh!!!! beat me to it

but obviously you also have to take into account pipe, fittings and all other resistances when calculating the correct size of pipe to use
 
Last edited:
my mrs does all our design work so she uses the cibse technical guides, it was the only book on her shelf that i understood enough to post details LOL!!
 
But the 40kw on 28 is fine. U can get it through 22mm according to guide! Doh!
 
you probably could but the increase in pressure and velocity would make it noisy - so she says....
 
Status
Not open for further replies.

Reply to Pipe kw carrying capabilities in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
153
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
259
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
207
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
361
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
274
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock