How critical is fiiting the right 'manual specified' nozzle on an oil burner?

Does the last letters matter much say between .55 80 EH or a .55 80 W ?

any comments?
 
Unless you've some experience and knowledge on oilers then follow the manufacturers advice. Putting the incorrect nozzle on, without setting up the air with a smoke gun , fga and oil gauges, can and will cause inefficient running of the boiler and a waste of fuel. The EH stands for Economy Hollow spray pattern and is a danfoss nozzle, W stands for Semi-solid spray pattern and is A delavan nozzle.
 
Any nozzles i use will be danfoss so will be mostly EH, ES, S and H, if i had to replace an EH and didnt have it an H would suit, if worcester approve it then it good enough for me!!
 
EH and ES can only be used on kerosene. So using s and h pattern nozzles in their place isn't a problem imho.

I never carry eh or es but then I mostly work on boilers running 35sec oil.
 
Sometimes not critical but you are better using what the maker recommends, H, EH, S, ES, or whatever, especially on a new condensing boiler.
Different nozzle makers, make what are supposed to be equivalent nozzles to other makers, but I find they can be entirely different & think it is best & easier to stick with identical make & type usually.
 
Exactly, if a manufacturer states 0.55/80 EH then it's because they've carried out extensive research on their boilers and burners using different nozzles to find the optimum performance. Also sticking the correct nozzle in means less faffing about setting up.
 
Tip - the Fluidics HF and SF anti-drip nozzles are handy as replacements for vintage burners where the anti drip mechanism has failed and they smoke on start up.
 
I paid about £7.50 for the last Fluidics nozzle I bought. About £2 more than Danfoss

Customer pays anyway
 
True, I could have sworn I paid nearer £15 last year though I dont get them that often.
 
Depends where you get them from. If your suppliers have to order in specially they'll pass carriage on to you.
 
My manual calls for a Danfoss 0.50 x 60W nozzle but I can only find Delavan in this size and pattern, would it be ok to use a different make?
 
That's including the VAT and with the carriage divided by the order. I think they are £3.50 list from HWOS

0.50 60W is a Delavan nozzle not a Danfoss. Probably a misprint. Use a 0.50 60EH instead
 
I went into my local plumb rip centre off t'other day for a 0.75 80 EH nozzle.

"£8.80 plus vat, please."

"HOW MUCH?"

"I'll see what I can do."

"£5.59 plus vat, please."
 
That's cheap compared to Plumbase!

Plumbase were going to charge me £12 for a 22mm equal compression tee. The builders merchants over the road has started stocking plumbing stuff due to Plumbase pricing and it's far more competitive.
 
Last edited:
I went into my local plumb rip centre off t'other day for a 0.75 80 EH nozzle.

"£8.80 plus vat, please."

"HOW MUCH?"

"I'll see what I can do."

"£5.59 plus vat, please."

That's still a complete rip off! I would have a word with them if I were you. Over here £5.59 + vat is still very expensive. Local Plumb Centre & others are very reasonable on Danfoss nozzles.
 
I had more than a word but I needed that nozzle there and then! I buy them from HWOS but I'd run out of this one and didn't want to use a different size.
 
Status
Not open for further replies.

Reply to Oil nozzles in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
481
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
293
Hi bit of a weird issue, I installed a grohe bathroom tap successfully 2 months ago bought from screwfix. Last week the right hand hot tap makes a squeak noise as I turn it on or off, left tap is 100% perfect and noiseless. This grohe tap is like one unit, so no screw notch or way I can remove...
Replies
4
Views
148
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
190
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock