S

stevew451

Hi customer complained when out to service of whistling noise when running bath tried no noise on kitchen tap or basin but on bath running noise was there thinking clean out hex any other suggestions ??
 
Check the basics, while running the hot tap is the noise definitely from the boiler? With the tap running, check the gas pressure, gas rate and telegan it too.


Sent from my iPad using Tapatalk HD
 
did all that during the service is definetly on the water side
 
Are you sure it's not the tank in the loft filling?


Sent from my iPad using Tapatalk HD
 
What model is it? I'm just looking at the 24HE and I'm struggling to see what may be causing this problem if its passed all its checks on a service, ie: high and low co2 readings. Can't see how cleaning the heat exchanger would help if the water temperatures are ok then i doubt there are any restrictions within the heat exchanger. You say it's only when the bath tap is running which would suggest its when the flow rate through the boiler is increased.
ImageUploadedByTapatalk HD1348338815.863542.jpg



Sent from my iPad using Tapatalk HD
 
The Baxi 105 used to have problems with noise from the diverter valve.


Sent from my iPad using Tapatalk HD
 
The Baxi 105 used to have problems with noise from the diverter valve.


Sent from my iPad using Tapatalk HD
instant not 105E,it was caused by the o rings,nothing in a duotec 1 really would make this noise the op is describing
 
instant not 105E,it was caused by the o rings,nothing in a duotec 1 really would make this noise the op is describing

That's right. It was the o-rings. What do you think this is then mate?


Sent from my iPad using Tapatalk HD
 
It has a domestic hot water filter.


Sent from my iPad using Tapatalk HD
 
do these have an inlet filter ??
yes 2 of them one under the loop connection if a internal type is fitted or under the cold inlet blanking cap if not the second is part of the hot water flow switch they can be a pig to remove this boiler is a duotec 1 and not the newer 2 is it?
 
Think there might be two filters



Sent from my iPad using Tapatalk HD
 
its a platinum 28he think this is the problem sh*t in the inlet gotta turn water off anyway to do a bit pipe alteration so might as well check while off
 
its a platinum 28he think this is the problem sh*t in the inlet gotta turn water off anyway to do a bit pipe alteration so might as well check while off
is the warranty up on it then?its a 5 year jobbie that said some plats are now 7
 
asked customer about that and no idea where info is doesnt even know where stopcock is ??
 
its a platinum 28he think this is the problem sh*t in the inlet gotta turn water off anyway to do a bit pipe alteration so might as well check while off

Let us know how you get on mate.


Sent from my iPad using Tapatalk HD
 
asked customer about that and no idea where info is doesnt even know where stopcock is ??
if its been registered Baxi will fix it FOC,as long as its been serviced,as you have just done that no issues
 