Have a kickspace which blows intetmittantly. Goes on for about 20 s then off and comes on again later only for short period again. Checked flow and return and appears return is only luke warm. New flexis replaced with a bigger bore. Could it be the kickspace that's blocked?

Thanks
 
It may have a temperature sensor on the flow pipe, which cuts out when the water temperature is below ( say ) 50C.
This is to stop the unit blowing cold air.

Either get the temperature of the water hotter for the unit to operate, or by-pass the temperature switch.
Some of these are 240 V connected inline with the fan - so be careful if by-passing switch.
 
If the heater is coming on then the water temp is hot enough, but not staying on long enough. Is this due to the return which could be restricted and in turn back up heat then knock the thermal switch off. What does the thermal switch look like
 
I'd say the heater core is partially blocked and needs cleaning out or replacing.

With the fan off there's enough flow through the heater to cause the stat / switch to switch the fan on.
As soon as the fan starts there's too much heat being blown off the coil and the fan will stop, coil temperature will rise, stat will switch, fan will come on etc etc.
The cycle will repeat for ever.

The waterways in those types of heaters are quite small and easilly block.

The simplest / cheapest way to fix it would be to remove the coil and take it to a car radiator repairer, they're used to working with the same type of coil.
They may be able to flush it out and or descale it, if not they'd be able to open the coil up and clean it out.

Check the price of buying a new coil then try a radiator repairer, see how it compares.
 
With these being at the low point of the system, they are prone to collect sediment as is being discussed.
Is the system water dirty?
It can be a case of balancing. Have there been any alterations?
Has this just happened or got worse over time?
Did it ever work well?
 
Lowest point on system, has worked previously but gradually proformance has deteriorated in terms of coming on sufficiently, water in system quite clean and no sludge,. Recently took off radiator for decotating and clean water with a little black sediment in it.
 
Took the heater out today, and possible cause is blocked return flexi, heater itself seems OK but washed it threw anyway. Return flexi unblocked using a bit of wire. Whisky isolator open.
Is there anyway of identifying which thd glow as nd return are on tje kickspace, myson have said its thd top
Hole but not hi g in the manual?
[automerge]1597949357[/automerge]
Should read with isolator valve open on flexi.

Is there a way of identifying the flow and return on the kickspace nothing in the manual.
 

Reply to Myson kickspace 600 blowing intetmittantly in the USA area at PlumbersForums.net

Similar plumbing topics

Hi All, In Dec 2023 I had my annual boiler service and asked the plumber to change 2 radiator valves as the radiator in the toilet downstairs was...
Replies
7
Views
530
I have just moved into a late 1990s new-build house with a small bore (about 1/2" OD pipes) gas fired boiler central heating system. All the...
Replies
4
Views
516
I currently have a Vaillant ecoTEC Plus 438 system boiler which is 13 years old. I have been having problems with the boiler which potentially...
Replies
6
Views
720
Hello all. I've just joined, was going to post in the new members forum, but the first site generated email sent me here... I am here, as have a...
Replies
21
Views
3K
N
Thanks in advance for any advice. We have a Lefroy Brooks XO concealed thermostatic valve shower and Worcester Heatslave 20/25 combi oil fired...
Replies
2
Views
1K
Nathalie
N
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock