Discuss My grant 70 mk 2 heating pressure is constantly increasing in pressure. I have changed the heat exchanger in the Oil and Solid Fuel Forum area at PlumbersForums.net

The E.vessel pre fill (air end) pressure should be 0.75bar with zero pressure at the water end, the filling valve should then be opened to give 1.25bar (cold system) , the pressure should then reach ~ 1.5 to 2 bar when system hot and will return to 1.25 bar when cold.
 
I'm fairly certain that model of grant should have a cold system pressure of between 0.5 bar to a max of 1 bar.
Expansion vessel pre charge 0.8 though later on in instructions tells you it should be 1 bar !
Remember that because it seemed a bit odd.
 
Grant used never give a pre charge pressure which was a bit daft as you have no water reserve to make up for tiny leaks etc without constant top ups but nearly always specified 1.0 bar filling, their PRVs are all set to 2.5 bar.
I set up a few neighbors to 0.75/1.25 bar and no problems in exceeding 2ish bar on heat up/
 
Ambiguous to say the least, it says pre-charged to 1 bar in one place and that the heating system vol is based on a "vessel charge and cold fill pressure of 0.5bar" in another reference.
By having the precharge&fill pressures the same means a much smaller vessel is needed, see my calcs below based on a average (of flow&return) of 65C. for a 50/90 with a 10 litre EV.

Its quite clear that the "temptation" is to have the precharge&fill pressures the same to avoid having to install a external EV especially since the boiler+stored vol of combis alone can be 40 litres, not so much a problem with the non combis with a boiler volume of 20/25 litres.

precharge/fill/final/system volume
0.5/0.5/0.86/106
1.0/1.0/1.48/106
0.5/1.0/1.70/106
0.75/1.25/2.0/106

Allowing final pressure of 2.2bar:
0.5/0.5/2.2/290
1.0/1.0/2.2/205
0.5/1.0/2.2/154
0.75/1.25/126



1635661965783.png
 
Last edited:

Reply to My grant 70 mk 2 heating pressure is constantly increasing in pressure. I have changed the heat exchanger in the Oil and Solid Fuel Forum area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
291
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
277
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days...
Replies
1
Views
206
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
196
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock